    Trane outside coil freezing up when cold outside
    I have a Trane made in 1986 model BWC036C100CA

    Only when it is cold around 40 degree outside the big coil freezes up and I get no heat. A/c and heat unit is up on roof, one unit. Im in phoenix, az.

    Maybe defrost is not working or bad board/relay not sure.

    Please advise

    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 2, 2009, 03:04 AM
    Maybe defrost is not working or bad board/relay not sure

    Could be the defrost board or a low refrigerant charge. If the A/C worked OK in the summer then I do not think the unit is low on refrigerant.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #3

    Jan 2, 2009, 04:29 AM

    Have you tried the emergency heat mode?
    Sproket's Avatar
    Sproket Posts: 10, Reputation: 1
    New Member
     
    #4

    Jan 2, 2009, 10:51 AM
    My thermostat doesn't have emergency heat mode on it. It is a older unit.

    Also the a/c did work pretty well during the summer and it does get pretty hot here.

    BUT during the summer when it is really hot outside above 110 the house will not get cooler than 83 degree's, the a/c unit can't keep up. It use to be a little better than that, cool the house down to around 79.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jan 2, 2009, 04:08 PM
    From the summer temp statement the unit seems to run fine. I believe you will find your problem in the defrost circuit.
    Sproket's Avatar
    Sproket Posts: 10, Reputation: 1
    New Member
     
    #6

    Jan 2, 2009, 05:26 PM
    I wonder what the defrost circuit consist of? Defrost board, relay? I need to find the diagram of the a/c heat unit layout.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Jan 2, 2009, 06:14 PM
    Look one the blower access or burner access door for diagram.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #8

    Jan 2, 2009, 07:43 PM

    83 is very good for any a/c I`ve ever seen, shouldn`t be any complaints there, guess refrigerant is OK,,
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Jan 2, 2009, 09:03 PM
    outside above 110 the house will not get cooler than 83 degree's

    Yes the A/C is doing great look at the TD between inside and outside.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #10

    Jan 2, 2009, 09:11 PM

    110 - 83 = 27. Gee... if I go "south" when I die, one of those would come in handy...
    Sproket's Avatar
    Sproket Posts: 10, Reputation: 1
    New Member
     
    #11

    Jan 2, 2009, 10:13 PM
    Well I should say 110-118 degree outside inside is 83. I know other peoples houses get colder than mine in the summer though. But really my problem is with the heater right now, coil freezing when it gets below 40 degree .


    I will look for diagram or call trane factory to get info.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #12

    Jan 2, 2009, 10:19 PM

    Check the control compartment at the outdoor unit for a literature packet. Trane is usually really good at providing info, but not so good at keeping it dry.
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #13

    Jan 3, 2009, 09:52 AM
    Quote Originally Posted by KC13 View Post
    Check the control compartment at the outdoor unit for a literature packet. Trane is usually really good at providing info, but not so good at keeping it dry.
    Or at making parts readily available :mad:
    Sproket's Avatar
    Sproket Posts: 10, Reputation: 1
    New Member
     
    #14

    Jan 3, 2009, 04:52 PM
    The paper diagram is toast, all weathered can't read and falling apart.

    Will have to find other means
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #15

    Jan 3, 2009, 06:23 PM
    Sometimes there are two, one inside and one outside the control compartment... did you look inside too?
    Sproket's Avatar
    Sproket Posts: 10, Reputation: 1
    New Member
     
    #16

    Jan 3, 2009, 07:51 PM
    The one inside was the one that is toast. Didn't see another
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #17

    Jan 3, 2009, 08:00 PM
    Say... I just had a service call last week, similar model and almost the same age. The defrost control would stop the outdoor fan but wouldn't power the reversing circuit or auxiliary heat. Try this: with unit running, locate the test terminals on the defrost control and initiate a forced defrost. See if the unit reverses to cooling and stops outdoor fan. Be careful of live electricity!
    Sproket's Avatar
    Sproket Posts: 10, Reputation: 1
    New Member
     
    #18

    Jan 4, 2009, 10:44 AM
    How is the proper way to force defrost mode? I am handy.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #19

    Jan 4, 2009, 12:39 PM
    There are test terminals like KC13 said on the defrost board. Jump them for a defrost.
    Sproket's Avatar
    Sproket Posts: 10, Reputation: 1
    New Member
     
    #20

    Jan 5, 2009, 10:55 AM
    OK, I usually jump with a piece of insulted wire stripped on ends. I will look for the test terminals and report back, may take couple of days

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

GE freezer coil freezing up unevenly [ 1 Answers ]

I have a Westinghouse Imperial ET18GKXSW02. The coil in the freezer gets an ice buildup at the first corner of the coil were the bi-metalic senser is located. The tubing is cold to that point. The reast of the coil stayes warm. No cold air but fan and comp. run

Spine Fin Coil on Trane [ 1 Answers ]

Looking at getting a Trane heat pump to replace an existing A/C unit. Heard some comments that the Spine Fin coil design Trane uses is difficult to keep clean and can actually clog up if not cleaned properly. I've heard good things about Trane overall but wanted to know if this design creates any...

Trane xl 80 heating system will not come on - below freezing outside. [ 6 Answers ]

Our Trane XL80 gas furnace will not come on. Turned thermostat all the way up and turned the fan to on. Nothing, no heat, now blower. Tried turning on the A/C and nothing happened. Followed the reset instructions and nothing happen. It seems to be dead. Help it is very cold outside, below...

Matching Coil - Trane XR-13 [ 2 Answers ]

Can someone give me a ballpark figure on the price of a matching coil for a new Trane XR-13 A/C?

Trane Variable speed w/hot water coil/Ac wiring ? [ 3 Answers ]

I've read many of the previous questions/answers, but haven't found what I need. Low voltage wiring is not my strong suit. My AHU has a hot water coil in it, that I plan to heat with a Voyager water heater. It has an A/C coil, and that works fine. Previous answers have said that I should find a...


View more questions Search