    Dec 31, 2008, 01:39 PM
    No heat from Trane XE 70
    I have a Trane XE70 furnace. I recently replaced the ignitor (it was abviously bad) and I now cannot get it to run at all.
    The ignitor glows, then the system cycles it off then on 3 times.
    The red LED then blinks constantly, no code just a constant flash.
    The gas valve is apparently not sending gas.
    What can I do to determine the problem? I can use electrical test equipment ( I have a Fluke vom).
    Thanks
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Dec 31, 2008, 01:57 PM

    Check the label on the module for a legend. In most cases a constant rapid flash indicates a polarity problem or a control diagnosed self-fault (replace control). Check for 24 volts at gas control during ignition trial period.
    JonL56's Avatar
    JonL56 Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 31, 2008, 07:47 PM

    Thanks, KC. There is no legend or I would have known that already.
    I have no voltage at the gas valve so I suspect the control unit may be at fault.
    I'll check the wiring and connections first tomorrow AM.
    Fortunately, I have a good standby heat source.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Jan 1, 2009, 12:08 AM

    Check for 24 volts at module gas control terminals during ignition trials. If output is measured at module but not at gas control, look for an open limit switch or fusible link.
    JonL56's Avatar
    JonL56 Posts: 3, Reputation: 1
    New Member
     
    #5

    Jan 2, 2009, 03:04 PM

    Thanks again KC.
    There was only 7.2 volts at the gas valve during cycling.
    To confirm the control was the problem, I jumped 24 volts from the thermostat connection (during the ignition cycle) and the gas valve opened, ignited and warmed the house just fine. Of course, I didn't leave it jumped this way.
    I found a control box this morning and installed it.
    The system works perfectly.
    Thanks a bunch!
    Jon

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane YCC low heat [ 2 Answers ]

We have a Trane YCC combined heat and AC unit (gas/electric) that has had some servicing recently after a couple of problems with the heating system. Now the unit is running properly (blower working, furnace producing heat from exhaust) but we have at best, low warm air coming into the house. The...

Trane Heater.blowing air, ONLY 62*F Heat [ 5 Answers ]

I have a 2002 Trane Electric Central Heater/AC. The heater portion has worked fine (maintains 70*F temp) since we moved into our new house, then all of a sudden yesterday it will not heat above 62*F. There is strong air coming from the floor vents on regular heat and emergency heat, but it does...

Trane XV 90 won't heat [ 3 Answers ]

Trane XV 90 won't heat. Fan runs, but just recirculates the (cold) air. I checked the covers on the unit -- they are in contact with the pressure switch. Brrr. Thermostat set to 68; inside temp is 59.

Trane central heat and air unit [ 2 Answers ]

Our air conditioner just suddenly stopped. The condenser will not kick on and we wold appreciate any suggestions to what the probem could be. It would be a great help if it were something my husband could possiblyfis.