    Fault Current At Commercial Main Service
    Here's a weird one. I have a tenant with a 150A, 3-Phase, 480V service. The main switchboard is in the basement and the breaker panel is located in the tennant's space 50 feet away. There is also a 120/208 panel board next to the 277/480 volt panel in the same closet. The step-down transformer is suspended above.

    Twice in the same year faulty HVAC equipment (480V 3PH) has grounded out and instead of tripping the branch circuit breaker, blows the main fuses in the basement. Once it was a 30 amp A/C device, the second time 9 months later it was a 60 amp duct heater. Again, neither time did the branch circuit breaker(s) trip, instead the main fuses blew. I don't suspect that the circuit breakers (newish) could be faulty although I have not had them tested. Could there be a grounding/neutral issue that is causing this problem... or possibly something else other than faulty breakers? Thanks.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Dec 15, 2008, 09:47 PM

    Explain "main fuse"? What size is it?

    The trip curves for breakers and fuses are very different. The fuse in general is a faster acting device. I'd compare the curves providing I understood the problem. "main fuse" was not defined and neither were the circumstances.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Dec 16, 2008, 03:34 AM
    I suspect the fuses are "One Time". This should be listed on the label. If so, to prevent this from occurring again, use "Time Delay" fuses, of the proper voltage and amp rating, which seems to be 600 volt at 150 amps.

    This will "coordinate" your overcurrent protection devices, that the proper device will open when necessary.

    You mentioned "fault current". There is a fault current rating of electrical equipment, fuses, breakers, etc, but has nothing to do with this situation, so the term is out of context. An explanation is a bit out of scope of this forum, but we can discuss it if you like.

    There are slower and faster acting fuses, and must be coordinated properly, esp when used in the same system as circuit breakers.

    Get back with the info on the main fuse, as Kiss requested, but be sure to provide make and model , not just the amp rating.
    MaintMan's Avatar
    MaintMan Posts: 11, Reputation: 1
    New Member
     
    #4

    Dec 21, 2008, 04:56 PM
    The three main fuses are 600 volt, 150 amp. Fuses are and were during both episodes dual element, time delay. I'm guessing that breakers are simply not tripping. Can't think of anything else it could be.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Dec 21, 2008, 05:15 PM

    Answer the question. What is the make and model of the breaker and fuse? You need to compare the trip curves of the fuses and the breakers

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

The right size for electrical service in commercial buildings [ 3 Answers ]

I am trying to understand how you calculate electric load requirements for commercial properties - how do I know if 120/208 or 277/480 is right and how do I convert needs for one service into another?

Short circuit current fault [ 1 Answers ]

I have quite a simple system. Contains one substation, feeder pillar and 3 houses. I have calculated the short circuit current that the transfromer in the substation can deliver but is there any one that can help me with finding the equations to calculate the short circuit current level supplied by...

200 amp main service panel [ 1 Answers ]

I am planning on upgrading my main service panel (in basement) to a 200 amp service, I want to put a 100 amp sub-panel to the attic for central air and all the lighting on the second floor(about 18 hi-hats and 4 fans). From the 100 amp sub in attic I also want to run a 50 amp breaker feeding a...

Main Service Panel needs [ 9 Answers ]

I ran across this site accidentally today and found someone who had many of the same issues I need help with. Most of my questions were answered reading the forum however I have one more, using the following information I am hoping someone can help. The existing house is apx. 2300 sq ft w/a 200...


View more questions Search