    Cable size required
    I have a house 60m from a transformer 240v single phase 50hz, and a shed which is 220m from the transformer. I want to run under ground power to both from the transformer. Is 220m to far to run this power to the shed, If not what size/type of cable do I require. The shed is not a workshop rather it will be renovated into a house at a later date.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 9, 2008, 03:48 AM
    Really need to know what the total maximum anticipated load in amperes, watts, or kilowatts, to do voltage drop calculations.

    Any wire installed will need insulation to be rated for wet locations first, if pulled in conduit, or rated for direct burial if that is the method used.

    I, and several others here only know American types of wire, we can give you wire size in metric, but will not know the types of insulation available to you in your country.

    Check with your local authority having jurisdiction over electrical installations for these types of wire, methods, etc. allowed. Get back with the loads and we can help size the wire. Ask the AHJ for any advice or requirements regarding voltage drop.
    AVRAAMG's Avatar
    AVRAAMG Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 18, 2008, 03:03 AM
    Before answering such question different factors must be taken into account.
    Not only distance. Usage of buildings must be known as well as the loads needed to be supplied. Methods od Installation of different circuits e.t.c.. Proper design must be made.

    Best Regards
    AvraamG

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cable size [ 1 Answers ]

what is maen 1x3x10 mm2 single phase?

Cable size [ 1 Answers ]

I have a 6.3kw hob for my kitchen, what is the smallest size twin and earth cable I can use to supply power to it?

What size Cable? [ 2 Answers ]

We're installing a Built-In Microwave Oven Combo unit, with specs as follows: 40 Ampere, 208/240 Volts, 60 Hertz (1/second). AC-ONLY. USE COPPER WIRE ONLY. A FOUR-WIRE OR THREE-WIRE, SINGLE PHASE ELECTRICAL SUPPLY REQUIRED Question: The new unit is approximately 35 feet from the breaker box. ...

Cable size [ 1 Answers ]

What size cable is required for 1450KW @415 v 3phase for 100metres with ambient temperature of 35 deg C


View more questions Search