    Rheem Classic 90 starts burner - then stops.
    I have a Rheem Classic 90 upflow heather. When it turns on the burner comes on fine but it stays on for just 5-10 seconds then shuts off. It does this twice then the blower comes on but with no flame going. The yellow flame sensor LED doesn't come on at any point. I have cleaned the flame sensor with steel wool. But apparently there is no power to the flame sensor. The two red LED's are on.
    Any ideas?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Dec 14, 2008, 05:09 PM

    Make sure you have a clean circuit to the sensor (not grounded), a solid ground to the burner assembly, and that all the burners are lighting.
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #3

    Dec 14, 2008, 06:12 PM

    Flame sensor could simply be shot.
    superlars's Avatar
    superlars Posts: 2, Reputation: 1
    New Member
     
    #4

    Dec 14, 2008, 08:43 PM
    Quote Originally Posted by MarkwithaK View Post
    Flame sensor could simply be shot.

    It's $12 so why not try replacing it. It looks fine though. The furnace worked fine last winter. This was the first time to start it up this winter. But I guess no yellow light speaks to either a faulty sensor or a bad board.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #5

    Dec 14, 2008, 09:12 PM

    Just replace it. I usually replace most flame sensors,unless I don't have one on the truck. You hate to have a call-back on a five dollar part. Check all of your connections.
    Frank Mangrum's Avatar
    Frank Mangrum Posts: 86, Reputation: -3
    Junior Member
     
    #6

    May 19, 2012, 09:57 AM
    Quote Originally Posted by hvacservicetech_07 View Post
    Just replace it. I usually replace most flame sensors,unless I don't have one on the truck. You hate to have a call-back on a five dollar part. Check all of your connections.
    Have you tried to check THE FLAME RECTIFICATION CIRCUIT?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

NO HEAT Rheem Classic 90 series 3 years old [ 6 Answers ]

I have a Classic 90 Series Rheem RGRA series upflow/downflow furnace 3 years old. Intermittently, the furnace will not flame up or give out heat. Sometimes it only blows cold air. Sometimes, it locks out (middle green light flashing once then pausing). The furnace repair company came out and...

Rheem HVAC classic 90 that will not light [ 2 Answers ]

I have a Rheem HVAC classic 90 that will not light The electronic igniter will not lit the burners I have changed the igniter and still will not work I can light the burners with a match but when it gets to temperature it will not light for the next cycle

Rheem Classic 90 duct cleaning [ 1 Answers ]

While I had the blower of my 10 year old updraft Rheem 90 HVAC system removed for inspection and cleaning, I noticed that above the fan in the duct there is a coil with black, gooey, fibrous material coating it on the bottom, which sloughs off easily. Is this an accumulation if dirt that should be...

Rheem Classic Clicking [ 1 Answers ]

I have a problem with my outdoor Rheem Classic 9 Heat Pump I just reciently changed the fan control relay, after a week of running it seems to be clicking. I problem I had before with the relay was it would not turn the fan. I can tell the clicking is coming from that relay. I don't know if...

Rheem Classic 90 Plus Blower start issue [ 11 Answers ]

The blower started acting up for few weeks. There was a several consistent short rumblings of the blower, something like half second on and half second off after ignition. Once the rumbling is over, the blower fan just works fine. I can also hear the relay inside the control box clicks when it...


View more questions Search