    Nov 13, 2008, 08:12 PM
    Thanks a lot. The new transformer blew the lights out in the house 30 sec after I powered it on. The load side was connected at that time. Do you mean that there is a chance that it will not burn if I do not connect the load side, and I will have time to read the voltage?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #22

    Nov 13, 2008, 08:59 PM

    Terminals look like figure 2 on this page:

    http://onlinecatalog.digikey.com/Web...PageIndex=361#

    A transformer of this size is incapable of blowing the lights. But the covers touching the primary side might cause some sparks if there are mechanical problems.

    Inspect all wiring. Make sure the transformer will be secure.

    You need to tape the ends of the wires that would go on the secondary and put your meter safely where the primary would connect and measure the voltage before permanently connecting the transformer.

    Wires should pass through grommets and wires should not be pinched.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #23

    Nov 13, 2008, 09:12 PM
    Thanks for the important info and the image, H.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #24

    Nov 20, 2008, 08:16 PM
    Still, cannot get the furnace running. I have measured the input voltage from the line - it is 122V. I installed two inline fuses. For the primary line the fuse rating is 0.5A, 250V. For the secondary: 3A, 32V (it's a car fuse). As soon as I turn the power on, the primary 0.5A fuse burns, the secondary fuse is OK. I am hesitant to install a stronger fuse as the power given to the primary line of transformer is already more than 40W (0.5A*122V). What else may be wrong? How come the power is so high? Appreciate any suggestion. H.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #25

    Nov 20, 2008, 09:18 PM
    I would start looking at something else than the transformer. The transformer problem is just the end product of the problem.

    First make sure the line and the neutral are not reversed both in the furnace junction box and in the house panel. Do not trust color of wires (Black/white) but check with a meter to be positive it is correct.

    If that is OK then disconnect all other 120 volt circuits that feed off the incomming line in the furnace except the transformer. Now activate the unit and see if the fuse still blows.

    If the transformer does not pop the fuse then the problem lies elseware in the furnace.

    Over the years I have seen circuit boards/motors both vent assist and blower/controls and relays cause similar problems and you will have to fish through them all till you find the culpret.

    I am sure by now you have disconnected all the thermostat wires at the thermostat itself and also disconnected all low voltage wires at the furnace to eliminate a low voltage wiring/thermostat problem. If not you may try that but when you said the short took out the circuit breaker for the furnace that would somewhat eliminate low voltage wiring since a short of that magnitude would have burnt that low voltage wiring to a crisp by now.

    Something is shorting to ground in that unit or circuit. These are the kind of problems I loved when I had the shop especially after 2 or 3 other companys could not figure it out. Over the years I have camped out at customers homes drinking coffee, smoking cigs and testing circuits till I finally figured it out.

    You will figure it out it is just a matter of time. Just isloate one component at a time.

    I used to carry mini circuit breakers used in the electronics industry so I could reset them and not keep blowing fuses.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #26

    Nov 20, 2008, 09:26 PM

    You don't need fuses in both the primary and secondary. There is an inrush current when the transformer is connected. The primary fuse MUST be of the slo-blow or time delay fuse if you decide to use one.

    Get yourself two 211-2 lamps from an auto store. These draw about 1A at 12V. Put them in series. And put the series connected lamps in SERIES with the secondary.

    This means that if connected in this fashion and connected to your furnace. If something was shorted in the furnace, the WORST that can happen is the bulb will light.

    BUT, remember that a bulb is worse than a transformer because it's inrush current is 10x times the normal draw.

    Trust me and connect the primary directly like it supposed to be connected, no fuse and connect the secondary to the two bulbs in series. Any bulb that draws from 1-1.5 at 12V will be fine. 1*24 = 24 W, 1.5*24=36 W.

    Complete the circuit. Show that this works. It will.

    Now cut the secondary circuit and connect the two ends where the secondary would go in the furnace. You just proved that the transformer can light the bulb with no problems so nothing bad will happen if something in the furnace is shorted.

    If something on the series connected secondary+2 bulbs+furnace shorts, the bulb lights.

    Start disconnecting things UNTIL the light goes out or severely dims.

    The bulb is a current dependent resistor. Since it's resistance when off is about 10X lower than when on, at low currents it's essentially a short circuit.

    IT WILL WORK!
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #27

    Nov 20, 2008, 09:36 PM
    hvac1000 and KeepItSimpleStupid: Really appreciate your input. I am in business again as there are several more things to check and work on. H.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #28

    Nov 21, 2008, 11:35 PM
    I have done some checks with two 12V bulbs in series (as suggested by an expert in one of the previous answers) and found couple of things I do not know what to do with, but think it might be important. I first connected all the elements in the secondary line in the following order: Transformer - Furnace - Lamps - 3A car fuse - Transformer. The bulbs were brightly lit. When connected in different order, Transformer - Lamps - Furnace - 3A car fuse - Transformer, the bulbs were out... because the 3A fuse burns right away. I do not know if this finding is of any use. When reconnected in the first order with a new fuse the bulbs are on again. I then disconnected the thermostats (two, connected in parallel) and the bulbs went out - the shortage eliminated? I am not sure if replacing thermostats will make it work, would it help? H.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #29

    Nov 21, 2008, 11:50 PM

    The order thing is a fluke. Bet the wires were touching at the bulb.

    Do the same thing, but disconnect the t-stats one at a time at the tstat to eliminate a wiring issue between the furnace and the stat.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #30

    Nov 23, 2008, 01:09 PM
    Well, I guess the problem has been located. As it was suggested in many responses, it turned out that the two-wire line of one of the thermostats was cut by and in contact with a sharp edge of the furnace's metal cabinet, hence the short circuit. Simply disconnecting that thermostat's wiring got the furnace running again. Thanks for all the help. H.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #31

    Nov 23, 2008, 01:31 PM
    Glad you got it going
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #32

    Nov 23, 2008, 02:09 PM
    Quote Originally Posted by harum View Post
    Well, I guess the problem has been located. As it was suggested in many responses, it turned out that the two-wire line of one of the thermostats was cut by and in contact with a sharp edge of the furnace's metal cabinet, hence the short circuit. Simply disconnecting that thermostat's wiring got the furnace running again. Thanks for all the help. H.
    I do believe I told you this a week ago lol. Glad you got it up and running.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

How much does furnace transformer cost [ 3 Answers ]

My furnace blower stopped working. I calle din a HVAC guy. He charged $159 for the transformer and $90 for the labor (30 minutes work). He calims the transformer blew out because of the A/C. the transformer he installed is 50VA 120-240. I can't believe this costs $159. Do these prices look real?

Repeated 24V furnace transformer failures? [ 26 Answers ]

Twice in two years, the 24V transformer in my furnace has failed. Both times it happened was after we had been away a couple of days and went to switch the heat back on at the thermostat switch. Our house is about 20 years old but this has just started happening the last two years. I have a...

GE furnace-One transformer or two? [ 1 Answers ]

I bought a programmable thermostat to replace my old one. It comes with instructions for hooking it up to a furnace with one or two transformers. The instructions are different depending on the number of transformers. My furnace is a GE model BWV936G110D0. I don't have the manual to find out if...

Where can I buy a 24v transformer for furnace? [ 2 Answers ]

Where can I buy a 24v transformer to replace on my Rheem furnace? I hear others talking about transformers costing $15-20. Where are you all buying these from?

No 24v output from a furnace transformer [ 3 Answers ]

Honeywell keypad without power, replaced transformer, control board is getting 120v but no 24v output, no fuse on the board (Rheem AC/Heat Unit)... any ideas


View more questions Search