    Identifing the first outlet in a branch circuit
    Any idea on how to identify the first outlet on a branch circuit. I need to install a GFGI outlet and in order to protect the rest of the outlets in the branch I need to put the GFGI on the first one. Also is there a minimum size outlet box to use when installing a GFGI outlet?
    Thanks,
    J:confused:
    schwim's Avatar
    schwim Posts: 132, Reputation: 22
    Junior Member
     
    #2

    Nov 14, 2008, 09:53 AM

    Hi there J,

    Someone may very well have a zoomier solution, but I would simply shut down the circuit, pull the recepts free from their boxes and alternate which one I disconnect, reactivating the circuit until I find out which one is the first in the chain.

    As for the depth of the box, I always go the max allowable by the particular situation, considering you don't have any other junctions in the box in question and you have an actual chain of recepts and not a single junction for all, you're dealing with two runs into the box and a fairly deep recept(GFCI). You can fit that in a standard depth box, but I've always been a fan of extra space for future pulls and I like the room to work.

    Thanks,
    Json
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Nov 14, 2008, 10:34 AM

    You use a little ingenuity and a breaker tracer. Once you know what outlets are affected. Guess how they might be wired. Assume a daisy chain.

    Use the binary approach. Disconnect the middle of the string.
    Then another middle etc.

    More like:
    Givens: Outlets served by breaker
    Possible path:
    Remove and disconnect a hot to eliminate outlets.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Nov 15, 2008, 11:17 AM

    Or you can save yourself all of the time diagnosing where the outlet string begins and replace the circuit breaker with a GFCI breaker and be done with it.
    Jwhitman's Avatar
    Jwhitman Posts: 3, Reputation: 1
    New Member
     
    #5

    Nov 16, 2008, 05:22 AM
    I would replace the breaker and be done with it except it has twin breakers or ganged breakers which ever term you want to use. The single breakers that are GFGI will not fix because the box is full.
    Thanks,
    J
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Nov 17, 2008, 07:34 AM

    J,

    If your main panel has no additional space and you are already using singles. You might want to consider installing a subpanel and then reducing the load on your main panel. This would also allow you to install a GFCI breaker in the sub panel.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

15 amp outlet on 20 amp circuit [ 5 Answers ]

Can I use a 15 amp outlet on a 20 amp circuit. Wire with 12 gauge wire.

Wiring multiple recessed light through branch circuit [ 7 Answers ]

I wired (11) recessed 4" incandescent cans in series with #12AWG on a 20amp circuit. After wiring was complete I noticed there was a note on the can that said "maximum of (8) 12AWG through branch circuit conductors" The maximum load on this circuit is approximately 12 amps. What is the...

Maximum load allowed on a branch circuit used for fixed resistance heating? [ 1 Answers ]

What is the maximum load allowed (%) on a branch circuit used solely for fixed resistance heating?

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...


View more questions Search