Load Calculation
I have a 100 amp switchbox.The left side has 6 slots ( 1 double switch 20amp, 1 double bar 30amp and 2 single 20amp. The right side has 3 double switch midgets at 20amps and 2 single 20amps. My question is how much can my box take and how do I calculate the usage?
|
|
 |
Uber Member
|
|
Nov 12, 2008, 06:10 PM
|
|
The amount and size breakers in a panel means nothing.
Need to know the square footage of all livable space, including basement if it can be finished, no garage, porch. And list of all major stationary electric appliances, size of any electric heat, AC, and we can do the calcs for you.
Or you can review Article 220 of the National Electric Code, see sticky at beginning of this forum. Read that a few times you will understand why electricians are like they are.
|
|
 |
Senior Member
|
|
Nov 12, 2008, 06:17 PM
|
|
I(E)=P
100(240)=24000W
-A 100A service will supply=24,000 watts
|
|
 |
Senior Member
|
|
Nov 12, 2008, 10:08 PM
|
|
how do I calculate the usage?
If you are trying to calculate the "total work" done. Then you would Multiply watts by total time during which the work (watts) is done.
Example: if a 60w bulb burns for two hours, then: 60w(2)=120 watt-hours. If trying to get total power consumed, then larger numbers will result. Example: Kilowatt-hours
Note: Check with your POCO for calculation methods. You can get the amount of power used per month off your utility bill.
|
|
 |
Uber Member
|
|
Nov 12, 2008, 10:29 PM
|
|
Let me confuse you a bit. 100 A means you have 100 A of 240 V available or 200 A of 120 V available if they were exclusive. I'm probably going to get in trouble for saying it this way.
The breakers have a distribution like every other one is on a different leg, so the way breakers are distributed could cause the main to pop.
Not sure why your asking the question.
A "load calculation" basically determines the service you need for a house.
With a 100 A service a hot tub is not recommended to be installed for example.
Panels are rated by the number of poles that they can accept. A pole can be thought of as the number of wires. This also can exceed the number of slots.
|
|
 |
Senior Member
|
|
Nov 12, 2008, 10:52 PM
|
|
100 A means you have 100 A of 240 V available or 200 A of 120 V available
I'll pass on making a big deal out of how you said it, and simply show this to clear "some" smoke for the reader:
100A(240v)=24000w
200A(120v)=24000w
|
|
 |
Uber Member
|
|
Nov 13, 2008, 05:36 AM
|
|
|
|
 |
Uber Member
|
|
Nov 13, 2008, 06:03 AM
|
|
I really am not following this line of answers. Seem to be off topic.
I am zoning in on the original question:
My question is how much can my box take and how do I calculate the usage?
Which means a Service Load Calculation will answer the question, once Derrick provides the information I requested.
|
|
 |
Senior Member
|
|
Nov 13, 2008, 07:31 AM
|
|
 Originally Posted by tkrussell
I really am not following this line of answers. Seem to be off topic.
I am zoning in on the original question:
My question is how much can my box take and how do I calculate the usage?
Which means a Service Load Calculation will answer the question, once Derrick provides the information I requested.
The op said: how do I calculate usage, so I take this as: How much power do I consume in a given period. Yet, the OP titled his question: Load Calculation
:confused::confused:
|
|
 |
Senior Member
|
|
Nov 13, 2008, 07:35 AM
|
|
 Originally Posted by KeepItSimpleStupid
Thank you! Unfortunately I'm well aware of James. :D :)
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Electric Load Calculation
[ 11 Answers ]
I have a Unit working at 6.5 Amps, 3 phase. I want to calculate the Power Consumption of the Unit. If I can get the formula by which the same is calculated.
The Formula is the most important.
I would be grateful, for a very quick reply.
Regards
Ujjval.
Wind load for signs calculation
[ 1 Answers ]
We have a specification for a sign to withstand 30 psf minimum lateral load. How can we calculate what wind speed this can resist (what mph and at what height)?
Load calculation
[ 1 Answers ]
There is a indoor pool and normally water is heated to temp 40 deg c. Total water quantity is 15000 ltrs. Out door temp is 44 deg c. The indoor a/c results in high amount of condensataion in supply grilles. FCUs are used to cool the area with 10% of fresh air. There is no possibility of untreated...
Load calculation
[ 2 Answers ]
Respected sir I amprakash ihave doubt regarding load calculation.
I have a 5 amp socket (ups power ) .can I connect 5 computors to that socket through extension box.please explain me any body knows
Load calculation
[ 1 Answers ]
Hi
Please advise me what are the factors considered for calculating the Tonnage Rate whilst selecting the AC units for Industry / office environment.
Regards
Pankaj
View more questions
Search
|