    Diagnostic light 4 open high limit device
    My funace reads 4 what dose open high limit device mean and how do I repair it TRANE
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 8, 2008, 09:46 AM
    Open high limit can be

    Dirty air filters
    Closed registers
    Blocked cold air return
    Blower motor problems
    High limit control defective or out of range.

    Look on the inside of the blower door for a wiring diagram. It should point the way to the high limit control. THIS IS A SAFETY DEVICE. Do not jump this control out of the circuit unless you are testing and then only if you have the proper equipment/tools to do the job.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane XR80 Furnace Open High Limit Device [ 16 Answers ]

I have a Trane XR80 furnace that has an LED flashing 4 times--Open High Limit Device. The filters are new and clean, I replaced the high limit switch, cleaned the flame sensor. Are there other switches I could check? Any other ideas? Thanks for any help or ideas. Brian

Trane xe 80 open high temperature limit switch [ 1 Answers ]

Furnace is about 13 years old... we just replaced the ignighter in it last night because it was running through all the steps to run except ignighting. It fired right up and ran for about 7-8 hours... now it won't ignite at all (it is running through all the steps it needs to except for...

High limit open [ 1 Answers ]

We have an Ultra V Tech 80 furnace. Cold air is coming out and the ignitors are not lit. Light is blinking 4 times which means high limit open. Where is this at? What needs to be done?

Diagnostic lights indicate pressure switch open because of reduced flow [ 1 Answers ]

My Carrier furnace is not starting for the first time this fall. The Diagnostic lights indicate pressure switch open because of reduced flow. Is there a re-set switch or some way to diagnose this problem. Is it possible there is something blocking flow? What can I do with this? In researching...

Open limit switch indicator light [ 1 Answers ]

I have a goodman furnace and just the other night I noticed the house wasn't heating, I checked the furnace and the indicator light suggested vent blockage checked the vent stack that leads to chimney and found 2 dead birds in stack removed them and started furnace, thought I had it fixed. All...


View more questions Search