    #1

    Oct 25, 2008, 12:54 PM
    Heil DC 90 - Pressure Switch Troubleshooting
    So far here's what I've got -

    1. Thermostat calls for heat.
    2. The inducer fan blows air.
    3. 24v is sent to the pressure switch.
    4. The pressure switch does not close (there is no voltage on the other side).

    Steps I've taken -

    1. Jumping the pressure switch allows the furnace to ignite and run "normally."
    2. I've checked the pressure tube for cracks, kinks, and clogs. Found nothing.
    3. I've cleaned the port on the inducer fan manifold - it was not clogged.
    4. Sucking on the tube from the inducer fan will close the switch.
    5. I've removed the exhaust and intake pipes. The inducer fan seems to be moving a good amount of air, but not creating enough negative pressure to close the switch. I don't have a meter to test the pressure in the tube.
    6. There was a bit of water in the pvc pipe coming from the inducer fan when I disconnected it. It seemed like condensation (I ran the furnace for a few minutes with the switch jumped).
    7. The condensate drain pipes seem to be functioning properly and not plugged up - some water has dripped from them.
    8. There doesn't seem to be any water in the tube or the switch.

    Any help would be appreciated!

    Thanks,

    Keith
    dale3's Avatar
    dale3 Posts: 12, Reputation: 1
    New Member
     
    #2

    Oct 25, 2008, 01:05 PM

    You really need to find out the actual water column (vacuum) reading and compare it to the pressure switch rating. Draft inducer could be running a little slow or sucking in air around the gasket area. Fan blades may also be bad.
    chefkeith80's Avatar
    chefkeith80 Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 11, 2008, 07:01 PM
    So, I built a manometer with water and measured the vacuum of the inducer fan. It read 2 inches of water pressure, but I'm not sure what the switch requires to close (it doesn't say anywhere on the switch).

    Today, there seems to be a bit of water in the exhaust pipe and there is definitely water in the inducer fan, and the furnace will not ignite (I had the pressure switch jumped and had ran the furnace for about 15 minutes today).

    Any thoughts?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Air pressure switch [ 1 Answers ]

If a air pressure fails and the fan stays on what will happen at the next demand.will ignition sequence complete or not.

Deep well, pressure tank/switch not building pressure [ 13 Answers ]

The only way I have water pressure is to leave the power on! I have replaced the 5 gallon pressure tank (28psi when void of water)/fittings/pressure gauge and tried 3 new 30/50 pressure switches and the problem remains the same. With the power off, the pressure drops to 0 (not 30). When I...

Troubleshooting Water Well Pressure/ Flow [ 2 Answers ]

I just bought a house and we are totally remodeling now I'm doing the plumbing we are going to have two full baths and 1 quarter bath/laundry. My problem is that after I got the bath/laundry every thing seemed fine then I installed all new every thing in the bath hooked up the water and no water...

Goodman limit switch/pressure switch? [ 2 Answers ]

Hi, I've got a goodman furnace (mod. # GHT070-3) it's about 5 years old. Recently, the heat will only kick on for about 30 seconds then shut off. It's giving me 4 flashes: Open limit switch, then it kicks off. After that it gives me 3 flashes and turns back on (pressure switch). It seems the...

Limit Switch - Pressure Switch [ 0 Answers ]

Hello Folks, This weekend I've been playing with a heating system at my new apartment and I'm trying to figure out what the different componets do. I kind of followed the circuit but still have some missing links... 1-There are some terminals on the furnace's circuit board labeled LIMIT. The...


View more questions Search