Jun 5, 2006, 10:31 PM
|
|
AC stopped cooling all of a sudden
My central air was cooling just fine all day. Around 5pm tonight the air coming out of the ducts wasn't cold any longer. I have a computer monitor the temps in the different rooms of the house and I noticed that all the rooms were cool (77-78) until around 5pm when the temps started climbing to 83 or so.
I checked the AC various times and the outside fan is spinning just fine. The air coming through the outside unit is cool instead of hot. The air coming out of the ducts is not cold at all. What would cause this to all of a sudden stop cooling. I can't imagine it would be a freon leak since that should take time. Any clues or suggestions? Could it be some drainiage pipe is clogged?
|
|
|
Senior Member
|
|
Jun 5, 2006, 11:12 PM
|
|
Filter plugged
|
|
|
Junior Member
|
|
Jun 6, 2006, 07:21 AM
|
|
Originally Posted by Demonspeeding_2005
filter plugged
Do you main the air filter? Or is there another filter. The air filter is one of those electrostatic filters set up on the return grill. The air seems to be coming out at the same force as before. If there is another filter where would it be?
|
|
|
Junior Member
|
|
Jun 7, 2006, 07:30 PM
|
|
Your fan outside is running but the compressor is probably not
There or numerous reason the compressor won't come on
|
|
|
Junior Member
|
|
Jun 7, 2006, 08:54 PM
|
|
Originally Posted by wheatnbarley24
your fan outside is running but the compressor is probably not
there or numerous reason the compressor wont come on
You are exactly right. The frustrating thing is that I paid for a AC company to come out and they tried to tell me it was a circuit board problem and that the compressor wasn't getting any voltage. They wanted to charge me for a new circuit board as well as the compressor. I checked the voltage myself and it was getting 24v when the fan is on. Now I have to wait 2 weeks to get a Sears to come out since I can't seem to trust anyone else. It is a Trane AC with about 8 years of service. Does anyone have any idea what this will cost? Will it be less than $1k or more?
|
|
|
Full Member
|
|
Jun 8, 2006, 03:25 PM
|
|
Originally Posted by jasv
You are exactly right. The frustrating thing is that I paid for a AC company to come out and they tried to tell me it was a circuit board problem and that the compressor wasn't getting any voltage. They wanted to charge me for a new circuit board as well as the compressor. I checked the voltage myself and it was getting 24v when the fan is on. Now I have to wait 2 weeks to get a Sears to come out since I can't seem to trust anyone else. It is a Trane AC with about 8 years of service. Does anyone have any idea what this will cost? Will it be less than $1k or more?
if you have 24 v going to the condenser unit, did the relay for the compressor pull in.. Do you have power 208 v + feed to the condenser unit.. did they test to see if the compressor is bad...
|
|
|
Full Member
|
|
Jun 8, 2006, 04:33 PM
|
|
There are many companies that would be glad to look at this for free and give you a quote. Call some places in your area, compare the estimates. You should be able to ferret out the BSer's. A compressor should last more than 8 yrs.
|
|
|
Junior Member
|
|
Jun 8, 2006, 07:18 PM
|
|
They didn't test the condeser. I will check to see if 208V feed measures OK. I would think so because the fan is going full blast and I hear the condenser motor start. The only thing the did was test the pressure to make sure there wasn't a leak. Unfortunately I wasn't home at the time they did 90% of their work. Thanks again for the help and suggestions.
|
|
|
Uber Member
|
|
Jun 18, 2006, 06:52 PM
|
|
Sounds like a classic situation where the compressor motor is not running, due to a faulty contactor (relay). Get it replaced and I bet your problem immediately goes away. Read my other postings on maintaining ACs.
24 VAC goes to the contactor's coil, which is controlled by your thermostat, and 220VAC goes to your compressor motor. The contactor points are probably shot and the compressor is not getting current.
|
|
|
Junior Member
|
|
Jun 21, 2006, 02:43 PM
|
|
How is the condenser fan getting current if the contactor didn't pull in?
|
|
|
New Member
|
|
Jun 22, 2006, 01:12 PM
|
|
Anytime I find a condenser fan motor operating and the compressor is not the first thing I suspect is a faulty compressor. It may be something as simple as a wire burnt off or something but it is usually a faulty compressor.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Sudden Violent Behaviour
[ 4 Answers ]
My dog is about nine months old. He is a neutered Husky Shepherd cross. He is normally a friendly kind albeit hyper dog. Tonight however, he lunged and snapped at my fiancé for no reason. Curtis (fiance) was sitting on the couch petting Nico (the dog) when the dog lashed out with his front paws...
A sudden change.. .
[ 24 Answers ]
The other night, my girlfriend of two years told me that she wanted to have a break. Now I have never had to deal with this so I am not quite sure what this means. She said she didn't love me anymore the way she did for so long and needed time to figure things out. However she did say she still...
Sudden loss of water pressure
[ 6 Answers ]
A couple of days ago I turned on the water at my kitchen sink and it came out with the usual force, but then about 10 seconds later it slowed down considerably. This continues to happen on both the cold and hot water, but I have not seen this happen at any of the other faucets in the house.
...
All of Sudden... Computer won't Start!
[ 4 Answers ]
Hi,
Yesterday I was working on my PC for couple of hrs. After I was done, I switched it off and left for some work. When I came back and tried to switch it on.. it won't start.
No fans wotsoever.. no cpu fan, no chasis fan, no smps fan. I only see a small led lighting up on motherboard....
View more questions
Search
|