    Wiring detached shop
    I am going to add a sub panel and wire my detached shop but have questions mainly about the neutral and ground connections.

    What I have is a 200A main mounted adjacent to my meter loop on the pole, then a panel mounted on the exterior of my house with breakers for things such as furnace, AC... etc. Then the panel inside that protects all the outlets, lights etc...

    Anyway, my plan was to install an 80 or 100A breaker in the Main panel on the pole and run 2-2-2-4 in conduit to a new panel in the detached shop (about 100' from the main). I know the two hots obviously go to the two lugs in the new sub-panel.

    Please clarify for me.

    1. The #4 ground from the Main panel will go to the added ground bar or neutral bar in the sub?
    2. The #2 Neutral from the Main panel will go to the Neutral bar in the sub?
    3. The grounds from the outlets & switches will go to the added ground bar in the sub?
    4. The neutrals from the outlets & switches will go to the neutral bar in the sub?

    Thanks in advance. I want it done right,
    David
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 5, 2008, 12:17 PM
    Quote Originally Posted by nitro901
    1. The #4 ground from the Main panel will go to the added ground bar or neutral bar in the sub? The added ground bar.

    2. The #2 Neutral from the Main panel will go to the Neutral bar in the sub? Yes. You DO NOT install the bond screw/strap.

    3. The grounds from the outlets & switches will go to the added ground bar in the sub? Yes
    4. The neutrals from the outlets & switches will go to the neutral bar in the sub? Yes
    Don't forget you will also need at least one ground rod at the detached structure and metallic water piping systems must also be bonded.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Sep 5, 2008, 12:36 PM
    Clarification for #2. Grounds and neutrals must remain isolated in any sub panel. Since you have a remote disconnect, it's very likely that your main panel is wired like a sub-panel and it has isolated grounds and neutrals.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Detached garage wiring [ 4 Answers ]

Built a detached garage in backyard, the underground line only allowed for 6-3 wiring. The 6-3 had to travel 110 feet to get to the sub panel in the garage. The garage is an 800 sq ft garage with a loft above it. The loft will eventually be converted into a small apartment. I plan on having a...

Detached garage pad [ 2 Answers ]

I am trying to get some information on building a garage starting with the Pad. I am planning on building a 22X26 detached garage. The rough grade was completed about 4 months ago. It is a clay base with no topsoil added yet. Should I get a bobcat in to remove a couple inches or just pack down...

Detached garage grounding rod or not [ 1 Answers ]

Hi, I just ran across another problem. I will be running 40 amps 240 volts out to my garage via underground 8-3 plus ground. Do I need a grounding rod at the garage or is the ground via the service cable to the garage enough? I have seen both and am not sure why. Is the 240 volt service to the...


View more questions Search