    Conductor size for 30AMP wall mount a/c outlet
    I am going to install a dedicated circuit to wall mount a/c, with the following details; single receptacle, 40' run, from distribution panel direct to outlet box, Have not acquired a/c unit, when I do, I will install adequate amperage breaker according to manufacturer's cut sheet. In the meantime I need to purchase conductor and install while wall is open. What would be the proper romex type cable to use? Thank you
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Aug 30, 2008, 06:46 AM
    #10 would be appropriate for a typical 30A circuit. You can run 10/2NM.
    I have to say, unless this unit will be HUGE, you will not likely need 30A
    561packrat's Avatar
    561packrat Posts: 80, Reputation: 1
    Junior Member
     
    #3

    Aug 30, 2008, 07:06 AM
    Quote Originally Posted by stanfortyman
    #10 would be appropriate for a typical 30A circuit. You can run 10/2NM.
    I have to say, unless this unit will be HUGE, you will not likely need 30A
    stanfortyman , thanks for prompt answer, probably overkill w/ the 30, 20AMP is most likely, would 12/2 nm be appropriate? Thanks
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Aug 30, 2008, 07:18 AM
    Yes, and since this will be a dedicated circuit you can convert it to a standard 120v/20a circuit later if you needed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to mount a wall mount pot filler [ 3 Answers ]

I was thinking about installing a wall mounted pot filler in our kitchen. What type of fitting and mounting does this require. I am using ½” copper to a thread male. I will secure the pipe to the stud. Is this correct. How far out does the thread need to stick out of the wall.

Adequate conductor size for art studio/ apt. [ 6 Answers ]

Converting detached garage to art studio/ apt. What is recommended conductor size to bring service from separate meter based on following:(1) approx. 70' including vert. run in 2' pvc, buried 2' to top. (2) anticipate 150 amp panel (3) My wife wants;tankless water heater, stove/oven,...

Range wiring - breaker and conductor size [ 4 Answers ]

This weekend I will be wiring a 120/240v 8,800 watt range (oven with 4 burners on top). My questions concern wire and breaker size. I've asked about this before and I still cannot determine the best answer. I understand that under the NEC, the minimum sized circuit for a range is 40 amp, using...

Service Entrance Conductor Size / Multiple Bonding [ 1 Answers ]

I am running service to a small, 1 room office, at a barn in the country. The electric utility pole has a transformer (230 V, 1 phase) and 200 amp meter. On the pole I have a 200 amp circuit breaker. From the circuit breaker on the meter pole, I have 4/0 4/0 2/0 AL cable in 2" PVC conduit...

Service conductor wire size [ 1 Answers ]

I am wiring a two-unit apartment that previously had fuse boxes for services. I am installing a two meter box outside to supply separate 200-amp rated main circuit breaker panels, one for each apartment. The calculated load for one apartment is about 102 amps, the other about 132 amps. What minimum...


View more questions Search