    Ground rod location
    I am running service to detached garage apt. Here's the basics: underground service from utility's pole to meter can at rear of house. Then directly adjacent and connected by 2" pvc , second , un-used meter can. From there 2" PVC under ground to new 200AMP distribution panel in interior of garage. I anticipate using 2/0 CU to new panel. I am un-clear if the new panel needs the neutral tied to the ground or if they remain separate and the grounding to earth at the garage. The service is currently grounde w/ ground rod at meter can. I have a retired building inspector who will check out my work and I WILL bring in a licensed electrician to do the stuff that is over my head, but I would like to have all my ducks in a row to minimize cost. Thanks
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Aug 29, 2008, 06:40 AM
    You will need a ground rod (or two) at the garage/apt.

    The water will also need to be bonded if the piping is metallic. If it is all or mostly pex or plastic then obviously no bond is required.

    From the meter to the main panel you need three conductors. Typically the neutral can be undersized. 2/0, 2/0, 1/0 CU is typical for 200 amps.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Leveling the ground with mulch for above ground pool [ 3 Answers ]

I was wondering if I could use mulch to level the ground for my above ground pool. I was told not to use sand, and I have a hard time digging.

Do you install a 120v 15 or 20 amp receptacle ground up or ground down? [ 15 Answers ]

Does the code have any stipulations on ground up or ground down? If so Prove it. An I am not talking about local ordinances nor the authority having jurisdiction. Simply the NEC.

Leveling ground for an above ground pool [ 2 Answers ]

I spoke to a pool company and they said that when installing an above ground pool you should "dish" the ground in the middle. This meaning that you make the ground in the middle of the pool 3 to 12 inches deeper than the rest of the ground. Everyone else that I have spoken to has said to level the...

Work location is different from employer office location [ 1 Answers ]

I work for NY based company and as an IT consultant. My actual work location is at the client's office which is in NJ for the whole of 2007. I also live in NJ. Will my income be considered as income earned in NJ or NY? My employer has withheld NY taxes though I live in NJ and my work location is...

Open ground when neutral not touching ground [ 3 Answers ]

Hi, I was moving around a room and noticed my wife wanted her desk elsewhere. I decided to, since she would have her computer on it, check the outlet she would be moving to. It seemed old so I changed it. I noticed before I changed it that with my GFCI tester, all sockets on this circuit were...


View more questions Search