Ask Experts Questions for FREE Help !
Ask
    kramwallace's Avatar
    kramwallace Posts: 9, Reputation: 1
    New Member
     
    #1

    Aug 28, 2008, 10:01 AM
    Is this a main panel
    Wiring comes in at meter then goes to 200 amp disconnect switch. Wiring goes from disconnect switch to panel in home. Would my panel in the house be a main panel or sub panel. I am asking because I want to add a sub panel to the home panel for a workshop. My panel in the house has the nuetral and ground together, is this right? The ground rod is at the meter, would the ground and neutral be together there and should the ground and nuetral at my panel in the house be separated with the neutral isolated? From reading this forum I think my house panel may need to have the neutral isolated, and I would isolate my panel for the workshop? If so I would run 4 conductor to the workshop and separate the ground and neutral and would I need a ground wire at the workshop since it is detached and is 50 feed away?

    Why not always separated the ground and neutral?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Aug 28, 2008, 11:50 AM
    This can be confusing because of terms.

    You panel is your "main" panel, but it is not the service disconnect. That is the switch outside.

    With very few exceptions, EVERYTHING downstream of the service disconnect must have the neutrals and grounds isolated.

    This being said, the panel is wired wrong. It SHOULD be wired as a "sub-panel", meaning the grounds and neutrals should be kept isolated.

    Also, any other panels fed from it should also be wired as sub-panels.

    You detached structure sub-panel also requires at least one ground rod using #6cu to the sub-panel.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Secondary panel from main panel electric [ 2 Answers ]

Can I use a number @2 aluminum ser 4 wires for a 100 amp sub panel?

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...

Connecting main panel to sub-panel? [ 1 Answers ]

I have my sub-panel for my workshop all set up, plugs & lites all wired in. The workshop isn't attached to the house & I was wondering what the best way was to connect from the main panel in the house to the sub-panel in the workshop?

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...


View more questions Search