    Back garage
    Hello all:
    Looking to run power to back garage about 170' from panel box. There will be no big loads in the garage (small compressor, lights, garage door, couple of battery tenders.

    Questions is can I run #4 wire off a 60 amp breaker into a panel in the garage. I will not have a main breaker in the garage but will have a few 20 amp breakers in there to power plugs and lights etc.

    Any help would be great.

    Thanks.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jul 16, 2008, 06:05 PM
    Back up, you need to do a rough determination of the load you need. 20 amp 30 amp you need to know that before connecting wires up. What is the total amperage being fed to the sup panel that is already in the garage?

    Can you help us please?
    kalvin's Avatar
    kalvin Posts: 3, Reputation: 1
    New Member
     
    #3

    Jul 17, 2008, 04:21 AM
    Garage is new.. 30 amps would be on the high side as this is a garage to park cars not a shop..
    Plan now is 60 amp dopuble pull breaker in the home panel running to a disconnect on the outside of the house then #4 wire urd to the garage panel with 2-3 20 amp breakers in it.. of course gfi for all plugs in the garage, and no gfi for the door opener.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jul 17, 2008, 07:27 AM
    Kal,

    If you are planning on a 170' run of 120/ 30 Amp from a panel in the same room, you will only need #10 AWG. Of course that's if the calculator I used is correct.

    If you already have a panel in the garage, why do you want an outside cut off. If there is an emergency, you want an emergency cut off as close to you as possible?
    kalvin's Avatar
    kalvin Posts: 3, Reputation: 1
    New Member
     
    #5

    Jul 17, 2008, 02:07 PM
    Don,
    Sorry I do not explain things very well.. The 170' is from the main panel box in the house running out to a sub panel in the detached garage which is new and has NO electric yet. Like I said the load is minimal as I have a shop elsewhere so this is for car parking and battery tenders, small 120v compressor etc..

    I am questioning the size of the wire from the house to the garage subpanel
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #6

    Jul 19, 2008, 05:00 PM
    #4 Alum will work, and is suggested for no more than a 170 ft run @ 30-40 amps.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #7

    Jul 19, 2008, 05:06 PM
    Please note that I'm considering volatge drop (Which is not required by NEC)
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #8

    Jul 30, 2008, 01:47 PM
    Kalvin,

    Perhaps you did not read my response correctly. You referenced a 60 amp breaker but you gave no indication of what the expected load would be.

    Also, You have to consider the voltage drop. On a 120 VAC line, the drop cannot be more than 3.2%. On a 240 VAC line, it cannot be more than 7.2%.

    All I did was ask you to tell us what the anticipated load would be. How does that merit a disagreement? Is it against some rule of yours to answer questions?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #9

    Jul 30, 2008, 01:57 PM
    Don, this post has the answer to your question:

    Quote Originally Posted by kalvin
    Garage is new .. 30 amps would be on the high side as this is a garage to park cars not a shop ..
    plan now is 60 amp dopuble pull breaker in the home panel running to a disconnect on the outside of the house then #4 wire urd to the garage panel with 2-3 20 amp breakers in it .. of course gfi for all plugs in the garage, and no gfi for the door opener.

    Use 30 amps to size the conductor for voltage drop at the 170 feet, and be done with it.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #10

    Jul 30, 2008, 02:00 PM
    Don, this post has the answer to your question:

    Quote Originally Posted by kalvin
    Garage is new .. 30 amps would be on the high side as this is a garage to park cars not a shop ..
    plan now is 60 amp dopuble pull breaker in the home panel running to a disconnect on the outside of the house then #4 wire urd to the garage panel with 2-3 20 amp breakers in it .. of course gfi for all plugs in the garage, and no gfi for the door opener.

    Use 30 amps to size the conductor for voltage drop at the 170 feet, and be done with it.

    Also you mis-spoke:

    Quote Originally Posted by donf
    he drop cannot be more than 3.2%. On a 240 VAC line, it cannot be more than 7.2%.
    You meant to say 3.6 VOLTS for 120 and 7.2 VOLTS for 240 volts.

    And, these are NOT mandatory, only recommended by NEC and IEEE.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #11

    Jul 30, 2008, 02:01 PM
    Kevin,

    That response from Kalvin was not in the item when I posted my response/question. Basically, Kalvin disagreed with my asking a question of him and then he entered the answer to my question. Go figure, no harm done unless you have a phobia about disagrees. Kev, here's the happy face again :) Don
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #12

    Jul 30, 2008, 02:05 PM
    I don't give a rats azz about disagreement comments.

    Or pay any attention to the little faces.

    You asked in post #2, the answer was in post #3.

    Also, did you see my comment about the Vd % and volts?
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #13

    Jul 30, 2008, 02:19 PM
    Quote Originally Posted by tkrussell
    Don, this post has the answer to your question:




    Use 30 amps to size the conductor for voltage drop at the 170 feet, and be done with it.

    Also you mis-spoke:



    You meant to say 3.6 VOLTS for 120 and 7.2 VOLTS for 240 volts.

    And, these are NOT mandatory, only recommended by NEC and IEEE.
    I agree 100%!
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #14

    Jul 31, 2008, 07:26 AM
    Kev,

    Yes, I saw your comments on the Voltage Drop.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Low cold water pressure in 2 showers... Not back to back config however [ 8 Answers ]

My home is 16 years old, I've had it for 5 years. I am on a pump - with 70LBS high cutoff and 55lbs Low turn on. All copper - I have 2 Delta 1600 shower faucets - one tub spicket with shower diverter - one shower only. The tub/shower combo has allways had only a trickle of cold water and...

How do I sync the keyless pad garage door opener to the main garage door opener? [ 3 Answers ]

I mistakenly gave someone my garage door opener that didn't return it. I had a male friend come over and "change the code" including my car opener and gave me a universial which he also programmed. I came to realize my code for my keyless pad outside doesn't work (since he changed the code... )....

Back child support and social security disability back pay [ 2 Answers ]

I live in Texas and I am making court ordered payments fro back child support for a non-minor child. I will be receiving social security disability soon and was wondering since I am making payments will my social security back pay be garnished?:confused:

From Pouring Garage Pad to Construction of Garage [ 4 Answers ]

How long to you have to wait after pouring the cement garage pad before you can begin construction on the garage?

2 periods back to back with large blood clots! [ 6 Answers ]

I have just stared yet another period after just ending one 5 days ago. I had major pain with the last one, I have never had that kind of pain before. Now with this period I just found an extremely large blood clot. Although it looked more like tissue then an actual bllod clot. What could this be...


View more questions Search