    Compressor shuts down too early
    My compressor unit shuts down before the thermostat is satified. It does cool down the house but in stages not at one time. It runs fine but will not run more than about 10 min straight. Fred
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jul 27, 2008, 01:05 PM
    Brand and model of thermostat?
    airfoil77's Avatar
    airfoil77 Posts: 3, Reputation: 1
    New Member
     
    #3

    Jul 28, 2008, 11:34 AM
    Quote Originally Posted by hvac1000
    Brand and model of thermostat?
    Armstrong SCU10 series by Lennox. Honeywell " Magicstat" model CT2400 Mike
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jul 28, 2008, 12:00 PM
    Is this the thermostat you have? If you turn it to fan on instead of automatic does the fan come on and continue to run?

    http://customer.honeywell.com/techli...0s/69-0789.pdf
    BocaRaton's Avatar
    BocaRaton Posts: 2, Reputation: 1
    New Member
     
    #5

    Jul 28, 2008, 12:04 PM
    My outside unit will go on for a fe minutes and die and the fan kept running... We ended up buying a new outrside unit that was it was not necessary, all we needed was the manual thrermosthat. We bought a $9.99 manual thermostat from Walmar t and try it... It is easy to install just follow the color cables...
    airfoil77's Avatar
    airfoil77 Posts: 3, Reputation: 1
    New Member
     
    #6

    Jul 29, 2008, 05:52 AM
    Yes this is the one. If the fan control switch is turned to on the fan does run. The only problem is that the high side shuts down too early. The thermostat still isn't satisfied for temp but the unit shuts down. If I'm only cooling one degree at a time you will not notice an early shut off, but if it needs to cool down perhaps three degrees it will shut off after cooling one degree. It's as though the unit is controlled by time not the thermostat. I wounder if an electrical device or pressure sensor is the problem. Heat works perfect . Mike
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Jul 29, 2008, 07:11 AM
    It could be the thermostat. Eliminate it from the circuit to force the A/C to continue to run uncontroled by the thermostat. If it runs and does not shut off then you will know it is the thermostat.

    Post back with your findings on this first test. Then we will go from there.
    designbo's Avatar
    designbo Posts: 4, Reputation: 1
    New Member
     
    #8

    May 30, 2009, 12:09 PM
    Quote Originally Posted by hvac1000 View Post
    Brand and model of thermostat?
    AprilAir is the brand of thermostat.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace runs then shuts off too early [ 8 Answers ]

My forced air furnace will run for around 5 minutes. Then it will stop but the servo motor will keep running. After another 5 minutes it will fire back up, the fan will kick in and it will start pushing heat. Then it will stop again some times within seconds, sometimes minutes. Does this sound like...

New Compressor goes on, shuts off immediately [ 5 Answers ]

I have a Trane EX1000 unit, compressor burnt up a few days ago. It just suddenly stopped being cool here, we were right into a 30 day plus run of over 90 temps. Unit has been cleaned, tech relaced a thermal expansion valve and installed new compressor. Compressor now will come on and then...

Compressor motor shuts off. [ 1 Answers ]

The compressor motor stopped running,(I was told it was bad) so I replaced it. When I started the unit back up it ran for a few minutes, but when the compressor tried to kick in it shuts off. I tried it several times but whenever the compressor tries to kick in it keeps shutting off. They gave me a...

Furnace shuts down early [ 1 Answers ]

I have a "Day & Night" gas heating/air 5 ton unit. When I turn on the heat in the morning all works fine but the unit shuts down before the desired temp. It's not the thermostat because I know enough to go out to the unit and bypass the thermostat. Nothing happens. After an hour or so, the unit...


View more questions Search