New Member
|
|
Jul 15, 2008, 08:07 AM
|
|
I have no power to two rooms in my house
I have checked the breaker box and there is no indication of a tripped breaker. The two romms with no power each have a breaker assigned.
|
|
 |
Uber Member
|
|
Jul 15, 2008, 03:03 PM
|
|
Hopefully it is just a 2 pole breaker triped. When 2 circuits share a neutral, both hots need to trip together. It would be a 2 pole 20 or 2 pole 15 amp breaker, Good Luck.
|
|
 |
Ultra Member
|
|
Jul 15, 2008, 05:43 PM
|
|
George... did this happen all of a sudden? Has there been flickering of lights or appliances in these two rooms? It's not uncommon for two circuits to share a neutral. Buy a cheap tester and check from the hot side of the outlet to the grounding screw. If you have power there, you have an open neutral, either at the panel, or at some junction box.
|
|
 |
Electrical & Lighting Expert
|
|
Jul 15, 2008, 06:00 PM
|
|
I suspect an open neutral of a multi-wire (shared neutral) circuit.
Probably a bad back-stab connection at a receptacle.
This is why the neutral of a MWBC is required to be pigtailed.
Does anything at all work? Do lights go up and down in brightness anywhere?
|
|
 |
New Member
|
|
Jul 15, 2008, 06:35 PM
|
|
How many outlets in these rooms?. any chance it's just the outlets themselves... seen it happen before... pull an outlet and test the wire's for power... just a thought.
|
|
 |
Electrical & Lighting Expert
|
|
Jul 15, 2008, 06:53 PM
|
|
 Originally Posted by gizmo_529
How many outlets in these rooms??.......any chance it's just the outlets themselves.........seen it happen before.......pull an outlet and test the wire's for power......just a thought.
Are you suggesting all the receptacles in two rooms all failed at the same time?? :rolleyes:
It is extremely rare for a receptacle itself to "fail" in the first place.
|
|
 |
New Member
|
|
Jul 16, 2008, 03:32 PM
|
|
 Originally Posted by stanfortyman
Are you suggesting all the receptacles in two rooms all failed at the same time??? :rolleyes:
It is extremely rare for a receptacle itself to "fail" in the first place.
Wasn't suggesting anything... just asked a question... who knows maybe its and efficiency apt with small rooms and only one outlet per room... lol... and I have seen more than one receptacle shot in a single room before... again... not the greatest apartment in the world... stranger things have happened... so roll your eye's at someone els pal!
|
|
 |
Electrical & Lighting Expert
|
|
Jul 17, 2008, 12:04 PM
|
|
Jeeze, what is with this crowd?
JustMarried614, you CANNOT be serious!
Connections fail, splices fail, it is rare for the receptacle itself to "fail", other than getting loose as far as plug grip goes. This typically does not affect the circuit though.
Where is YOUR professional reply to this thread??
Gizmo, sorry PAL, you certainly were suggesting that.
What do you think the possibilities are that all the receptacles in two rooms all failed at the same time? THAT was my question. That's all.
|
|
 |
Home Improvement & Construction Expert
|
|
Jul 17, 2008, 02:33 PM
|
|
George
Suggest that you remove one of the non working outlets. See if it has been wired using the little holes in the back. Called back stabing. These are known to develop poor connections after a period. If you find this wiring methord was used, rewire all of the outlets using the screws on the side. Rewire all outlets and switches including the ones that work. The bad connection can be where the last working outlet feeds the non working outlet.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Power for house
[ 2 Answers ]
How do you figure out how much power is needed for the whole house?
Mobile Home - Lights and power not working in certain rooms.
[ 6 Answers ]
My husband isn't mechanically inclined and I rent my home from a ghetto landlord who says for me to fix things and send him a bill. So I live in a 1500 sq ft. mobile home, and right now my power to one of my bathrooms, my dining room and my sons room will not work. The TV in my sons room that is...
Losing Partial Power to house.
[ 4 Answers ]
I keep losing power to several rooms, appliances in my house. The power goes out, doesn't trip any breakers, then in 1-2 hours, it comes back on. It seems to be several circuits effected, not just one, but I'm at a loss as to what might be causing this. I have tested the power coming into the...
Power in part of house goes dead w/out triping breaker
[ 3 Answers ]
Hello, great site, use it more than I thought I would.
Question: The electricity in part of my house will go dead without tripping the breaker for those rooms and then will come back on within 30-60sec by itself, lights have been dimming as if a dip in voltage has occurred.
Thanks
Gbrown
View more questions