Ask Experts Questions for FREE Help !
Ask
    JuJuFruit's Avatar
    JuJuFruit Posts: 45, Reputation: 3
    Junior Member
     
    #1

    Jul 9, 2008, 04:17 PM
    2 capacitors? Which wires go where?
    Hello, After 3 days we have deduced that our fan motor was bad. I purchased a new one today.

    We were told to get another capacitor, and to leave the old one connected as it ran the compressor?

    the old motor had 3 wires. Black, Orange, and brown.

    the orange and brown are going into the capacitor.

    the new motor has 4 wires. Black, white, brown, brown/white


    I have been googling and I am lost.

    The place where I bought the new motor, told me this

    Black = black
    White = Orange
    And browns go to the capacitor.

    BUt he didn't say WHICH the old or the new.

    We are just confused and hot, which wires go to the old capacitor? And which go into the new one?


    The old was a 5 and the new is 7.5
    JuJuFruit's Avatar
    JuJuFruit Posts: 45, Reputation: 3
    Junior Member
     
    #2

    Jul 9, 2008, 04:30 PM
    Also it is a 4 ton rheem. We had an AC guy come out and after trial and error he told us it was the fan motor.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #3

    Jul 9, 2008, 04:33 PM
    Brown and brown white go to the cap. Other to go to the contactor. The old cap should have a wire that goes to the compressor marked (HERM) and a common that will go back to the contactor, add the new cap, hook the two brown wires from the new fan motor, one on each side, black and white wires go to the contactor where the old orange and black wires were hooked up.
    JuJuFruit's Avatar
    JuJuFruit Posts: 45, Reputation: 3
    Junior Member
     
    #4

    Jul 9, 2008, 04:35 PM
    OK so the black is hot. The SOlid White goes to the "OLD" one where the Orange wire was?


    Just want to make sure cause if hubby burns up this motor we are in for a HOT night.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #5

    Jul 9, 2008, 04:38 PM
    Yeah, balck and white are both hot legs, hook the white wire where the orange wire was, hook the black wire where the black wire was
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #6

    Jul 9, 2008, 04:39 PM
    The only thing different is the two brown wires from the new fan motor are going to the new cap.
    Credendovidis's Avatar
    Credendovidis Posts: 1,593, Reputation: 66
    -
     
    #7

    Jul 9, 2008, 04:41 PM
    Well : I have to guess also a little, as there is not enough information to provide a sure reply.

    You stated : "the old motor had 3 wires. Black, Orange, and brown. The orange and brown are going into the capacitor".

    That would be one wire short. If orange and brown only go to the capacitor, all that remains to power the motor is the black wire. Where is the second power wire connected to? It seems that the black wire is the "hot" wire, while the orange wire is (or is connected to) a neutral wire. There should be somewhere another orange or white wire, either at the capacitor or at the motor.

    Note 1 : Normally power is connected to one side of the capacitor : when power is connected to one side of the capacitor the motor will turn clockwise, but when power is connected to the other side the motor will turn anti-clockwise.

    ===

    You stated : "the new motor has 4 wires. Black, white, brown, brown/white"
    And also : "The place where I bought the new motor, told me Black = black.
    White = Orange. And browns go to the capacitor
    ".

    In that case black is hot , white is neutral, and the browns are going to the capacitor. Just make sure that there is no third wire connected to the capacitor (as possibly is done in the old configuration!)

    Note 2 : the white wire is actually the orange wire in the old configuration.
    As stated : somewhere a neutral wire must be connected to the system. In the old system that was the orange wire, or connected to the orange wire. In the new system the neutral goes to the white wire.

    Hope this helps ! Success !

    :)
    JuJuFruit's Avatar
    JuJuFruit Posts: 45, Reputation: 3
    Junior Member
     
    #8

    Jul 9, 2008, 04:43 PM
    Thank you so much.. its 92 in our house right now.

    One more question if you could.

    We had a LMT that controlled the time delay. The first AC repair guy said the LMT was the cause of our unit shutting off. The electric company came out and removed the LMT.

    Now we do not have a time delay on our Unit. I bought one today. And the guy said it was easy to install. However hubby doesn't see where to install it. Any Ideas?
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #9

    Jul 9, 2008, 04:45 PM
    Is it 24 volt? Most of the new digital thermostats have time delay built in. What type of a stat do you have?
    JuJuFruit's Avatar
    JuJuFruit Posts: 45, Reputation: 3
    Junior Member
     
    #10

    Jul 9, 2008, 04:47 PM
    We have a digital thermostat inside. But this is a 5 minute time delay that is for the outside unit. To be mounted inside of the unit.

    I will run outside and ask about the voltage
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #11

    Jul 9, 2008, 04:48 PM
    Quote Originally Posted by Credendovidis
    Well : I have to guess also a little, as there is not enough information to provide a sure reply.

    You stated : "the old motor had 3 wires. Black, Orange, and brown. The orange and brown are going into the capacitor".

    That would be one wire short. If orange and brown only go to the capacitor, all that remains to power the motor is the black wire. Where is the second power wire connected to? It seems that the black wire is the "hot" wire, while the orange wire is (or is connected to) a neutral wire. There should be somewhere another orange or white wire, either at the capacitor or at the motor.

    Note 1 : Normally power is connected to one side of the capacitor : when power is connected to one side of the capacitor the motor will turn clockwise, but when power is connected to the other side the motor will turn anti-clockwise.

    ===

    You stated : "the new motor has 4 wires. Black, white, brown, brown/white"
    And also : "The place where I bought the new motor, told me Black = black.
    White = Orange. And browns go to the capacitor
    ".

    In that case black is hot , white is neutral, and the browns are going to the capacitor. Just make sure that there is no third wire connected to the capacitor (as possibly is done in the old configuration!)

    Note 2 : the white wire is actually the orange wire in the old configuration.
    As stated : somewhere a neutral wire must be connected to the system. In the old system that was the orange wire, or connected to the orange wire. In the new system the neutral goes to the white wire.

    Hope this helps ! Success !

    :)
    The orange wire was being fed by the common terminal on the ol cap, this is a pretty common practice with many brands.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #12

    Jul 9, 2008, 04:51 PM
    I would focus on getting your air on first, add the time delay later
    JuJuFruit's Avatar
    JuJuFruit Posts: 45, Reputation: 3
    Junior Member
     
    #13

    Jul 9, 2008, 04:51 PM
    This is for power surges. Said to mount timer in control panel, connect wires to relay.

    Which wires. There are 2 yellow (different shades) of wires that have wire caps on them. No other wires are just there without being coneected to anything
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #14

    Jul 9, 2008, 04:53 PM
    The control panel is the electrical compartment on the air cond. Unit. What is the voltage on the delay?
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #15

    Jul 9, 2008, 04:59 PM
    If it is 24 volt, just break the thermostat wire that has 24 volts on it coming into the unit.
    JuJuFruit's Avatar
    JuJuFruit Posts: 45, Reputation: 3
    Junior Member
     
    #16

    Jul 9, 2008, 04:59 PM
    Its says input for 1 wire, and Load for the other wire.

    This is a delay for the breaker. 240 volt

    Linebacker
    Solid Stae
    Delay TImer
    Fixed 5 Min
    Short Cycle Protection - single Phase
    Pro.no.EAC - 501-300 (18-288VAC0
    Delay on break


    That is what it says on the package
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #17

    Jul 9, 2008, 05:03 PM
    So you need to break one leg of the power feeding the unit, either at the breaker box or the unit.
    JuJuFruit's Avatar
    JuJuFruit Posts: 45, Reputation: 3
    Junior Member
     
    #18

    Jul 9, 2008, 05:05 PM
    Right, to protect the unit from the power surges.


    But hubby does not know where it installs. Since there was not one on it before.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #19

    Jul 9, 2008, 05:09 PM
    Mount it on the inside of the unit, shut the power off, cut one of the main power wires, connent the side coming in to input and the other to load.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #20

    Jul 9, 2008, 05:15 PM
    How would you install it? Instead of giving a "bad rating", offer some advice smart guy.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Capacitors for a ceiling fan [ 1 Answers ]

Does anyone know where I can buy a capacitor for a Hampton Bay ceiling fan? Home Depot and Lowe's don't carry them. The problem that I am having is that the ceiling fan only has one speed. I changed out the switch but it is still running on one speed. I was wondering if it is the capacitor. Hope...

Bad capacitors [ 4 Answers ]

I have a goodman a/c I replaced the capacitor about three months ago and found the samr problem today, can anyone tell me what might be causing this problem.

Capacitors [ 5 Answers ]

Hi, Can someone please help me with this question. I'm not sure if I have it all horribly wrong or not... Please refer to the attached picture "capacitance.jpg". With a current moving from A to B and the several capacitors between the idea is to find total capacitance from A to B. Here...

Capacitors [ 1 Answers ]

Hello all, I have a capacitor problem that I can't seem to get a handle on. Maybe someone out there has some ideas. Ok... you have an AC source. It provides 25V (rms) with frequency of 580 Hz. There is a capacitor connected across its terminals. When a second cap. Is connected in parallel...


View more questions Search