    Intermittent Compressor
    I have a Carrier Condenser It requires 197-253 Volts, 30 Amps. I have tested my incoming voltage, which is 249 Volts.

    The Hvac guy who installed it said I might need a Hard Start Kit, to give the compressor the extra power it needs. It is a 5 year old unit that was installed a month ago. The fan on the condenser always goes on, but the compressor is intermittent.

    My issue with his advice, is that when he installed the condenser, and breakers he split the breakers, one at the top of the panel and one at the bottom of the panel, which theoretically should work because they land on different phase of my panel, but is against code. He installed 2 30 amp single pull breakers. Any ideas would be appreciated

    Thanks,

    Joe
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jun 22, 2008, 11:33 AM
    Why would you take seriously the advise of some one who did such a unprofessional job as that. Is there such a thing as a Hard Start Kit? If it is a very long run from the electric panel to the compressor it is possible that the wiring is undersized. Also possible that you have a faulty contactor.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Jun 22, 2008, 03:41 PM
    The Hvac guy who installed it said i might need a Hard Start Kit,

    Yes they are available but should be installed by a competent person.


    It is a 5 year old unit that was installed a month ago.

    Was this a used unit?

    and breakers he split the breakers, one at the top of the panel and one at the bottom of the panel, which theoretically should work because they land on different phase of my panel, but is against code

    This is beyond code. This is a disaster waiting to happen.

    He installed 2 30 amp single pull breakers

    A dual handle 220 volt breaker must be used with both breaker handles tied together just as it comes from the factory.

    Get a person that knows what they are doing.
    Elwoodslc's Avatar
    Elwoodslc Posts: 3, Reputation: 1
    New Member
     
    #4

    Jul 2, 2008, 12:34 PM
    Thanks for the quick response.

    Was this a used unit? Yes


    he split the breakers, one at the top of the panel and one at the bottom of the panel, which theoretically should work because they land on different phase of my panel, but is against code

    This is beyond code. This is a disaster waiting to happen.

    He installed 2 30 amp single pull breakers

    A dual handle 220 volt breaker must be used with both breaker handles tied together just as it comes from the factory.

    Get a person that knows what they are doing.


    I understand that this is a problem that I have already fixed myself. My question is if I need a hard start. My Voltage is still 249V. Which makes me wonder what a hard start would due, because my Condenser is rated for 253V MAX. Would a hard start damage the condenser. My HVAC guy also said when this particular model of Carrier condenser came out, that they all needed a hard start.

    So any help would be appreciated

    Joe
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #5

    Jul 2, 2008, 02:27 PM
    My HVAC guy also said when this particular model of Carrier condenser came out, that they all needed a hard start.(quote)


    Instead of talking,why didn`t he install one,, they not that expensive
    Elwoodslc's Avatar
    Elwoodslc Posts: 3, Reputation: 1
    New Member
     
    #6

    Jul 2, 2008, 02:30 PM
    Quote Originally Posted by wmproop
    My HVAC guy also said when this particular model of Carrier condenser came out, that they all needed a hard start.(quote)


    instead of talking,why didn`t he install one,,,,they not that expensive
    He didn't have one on his truck and his distributor was closed.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Jul 2, 2008, 03:01 PM
    Many older Carrier units come with a hard start kit already installed from the factory. This is done by design and is a necessary part for the use of the equipment. My 30 year old Carrier/Bryant unit came with a hard start system installed and over the years I have had to replace both the relay and capacitor in the start kit and the contactor. Other than that it has been trouble free. That is a great track record for a 30 year old unit. Good luck with your repair.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Intermittent cooling [ 5 Answers ]

I have a fairly new Carrier AC, serviced regularly. Each time it is checked, the service man says all is working well. Then the hot spell comes, and I can get no cool air during the hottest part of the day, and it comes on and works just fine in the late afternoon through evening. I did have a...

Intermittent blower [ 5 Answers ]

Today was the first day I turned on the A/C. and I'm having an intermittent blower motor problem. Everything comes on fine, but the blower motor inside the house will only run for a minute or two then shut off, but the ac unit outside keeps running? Anybody have any idea what I need to check?.

Heat is intermittent [ 2 Answers ]

I have a York hvac system. AC works great. Heat is intermittent. I'll turn it to heat on thermostat and it may run for a while, but at some point (inconsistent as to how long), it turns from blowing warm air to blowing cold air. At times, I am able to turn everything off at the thermostat,...

Intermittent power [ 1 Answers ]

I have a client who has a triplex service drop rubbing on some tree branches. They have removed some brick facing on the exterior of the house exposing conductors running from the main service panel in the basement on the outside of the structure and into a slab addition at the rear of the house. ...


View more questions Search