    a/c unit does't work
    Hi, my name is mike and I have a lennox a/c unit that won't kick on , the inside blower
    Fan works but out side fan doesn't. All I hear is a click. A friend told me to replace
    The capacitor first. I replaced it and have the same problem.
    twinkiedooter's Avatar
    twinkiedooter Posts: 12,172, Reputation: 1054
    Uber Member
     
    #2

    Jun 11, 2008, 10:28 AM
    Try replacing the relay switch. That was always the problem when my outside unit would not run but the inside fan worked.
    poorboy2's Avatar
    poorboy2 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 11, 2008, 10:49 AM
    The click you hear means that your transformer and thermostat are working.

    That click means the contactor is closing and should pass power to the outside fan motor and compressor at the same time, thus a supply power problem

    This leeds me to believe that one of the contact points are burned or a burned wire @ the contactor. There could be a combination of bad fan motor and comp. but not likley

    If you open any panels on A/C turn the power off FIRST!!

    More information is needed as what if any sounds are heard after the "click"
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jun 11, 2008, 11:28 AM
    Check fuses or circuit breakers for the outside unit.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #5

    Jun 12, 2008, 10:52 AM
    The contactor can kick in meaning you have low voltage power to contactor,, but if you don`t have high voltage nothing will come on the contactor is probably fine,, check breakers and /or fuses,if OK check for 220/230 volts going in and coming out of the contactor with the contactor kicked in,, also check capicitor,, beware be careful,electricity can jar your teeth and other vital body parts

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

AC outside unit doesn't work [ 3 Answers ]

Hello, I have a simple question. I had a guy replacing the board on our hvac a few motnhs back to fix the heat. Today I turned on the AC for a first time this year and the outside unit did not start at all ( the fan on the inside unit is blowing ). I opened the system and I saw two wires going...

Does anyone know if you can borrow against a 401k if the employer does't make loans [ 4 Answers ]

Does anyone know if you can borrow against a 401k from anyone if the employer does not make loans against a 401k

AC unit That does not work [ 2 Answers ]

I opened the compartment to the outside unit and there were three things. A circuit board, something that looks like a small canister and a switch that looks like a relay. The circuit board has a flashing green light. When it is switched to cool there is a click followed by another click. But...

AC unit That does not work [ 1 Answers ]

When I set the thermostat to on there is a click on the outside unit but it still will not come on. Anything else. The outside circuit braker is a manual breaker, that can not be shut off through over load or short. To break this circuit, you have to remove the jumper which is in a good state. ...

My AC unit does not work [ 2 Answers ]

I owned a Carrier AC. The outside fan does not spin or work. The indoor thermostat control did not or has not shown any error message. I have checked out all circuit breaker and all tested OK. Is there a fuse somewhere I don't know about? What did I miss? Thanks


View more questions Search