    Outside Electric
    I have outside electrical box that is approximately 30 years old. It has 2 lines going in . 2 blacks , 2 whites and grounds coming in. Can I install 2 gfci outlets in there ?
    mr500's Avatar
    mr500 Posts: 181, Reputation: 8
    Junior Member
     
    #2

    May 23, 2008, 05:20 PM
    Yes, But why? Is this a 2 gang box? I say this because you can install 1 gfi and it can protect anything downstream.

    Other words if you want 2 receptacles, install 1 gfi and the 1 regular plug, and the gfi can protect both.

    If that what you want to do. No need in buying 2 gfi's for the same box.

    Just wire the incoming power pair up to the LINE side and the other receptacle into the LOAD side of the gfi. Now your protected with only 1 gfi.

    Hope that helps

    Mike
    rsrcwhite's Avatar
    rsrcwhite Posts: 16, Reputation: 1
    New Member
     
    #3

    May 23, 2008, 05:23 PM
    I don't know how to nstall another outlet ''downstrem''
    mr500's Avatar
    mr500 Posts: 181, Reputation: 8
    Junior Member
     
    #4

    May 23, 2008, 05:25 PM
    Quote Originally Posted by rsrcwhite
    I dont know how to nstall another outlet ''downstrem''

    OK. When I say downstream I mean on the other side of the gfi. Your power comes in from the panel to the gfi first. Then anything after that is "downstream".

    Is this a 2 gang box? Is the box big enough for 2 receptacles I mean?
    rsrcwhite's Avatar
    rsrcwhite Posts: 16, Reputation: 1
    New Member
     
    #5

    May 23, 2008, 05:36 PM
    Yes... it is a 2 gang box. It has a switch and outlet. It seems to have 2 sets of wires coming in to it.it looks like the switch works both theoutlet and another outlet that was there but is no longer there. The line is still active. It was once used for an inground pool.
    mr500's Avatar
    mr500 Posts: 181, Reputation: 8
    Junior Member
     
    #6

    May 23, 2008, 05:39 PM
    Quote Originally Posted by rsrcwhite
    Yes...it is a 2 gang box. It has a switch and and outlet. It seems to have 2 sets of wires coming in to it.it looks like the switch works both the outlet and another outlet that was there but is no longer there. The line is still active. It was once used for an inground pool.

    OK. And you want to install 2 outlets in the box correct? And you have a total of 2 romex wires coming into the box, as I read. Do you have the gfi bought? You only need one. And a new outlet if you don't have one and you can get started.
    rsrcwhite's Avatar
    rsrcwhite Posts: 16, Reputation: 1
    New Member
     
    #7

    May 23, 2008, 05:49 PM
    I haven't bought anything. Just wire both outlets separately? Thanks
    mr500's Avatar
    mr500 Posts: 181, Reputation: 8
    Junior Member
     
    #8

    May 23, 2008, 05:58 PM
    Quote Originally Posted by rsrcwhite
    I havent bought anything. Just wire both outlets separately? Thanks

    NO not seperatly per say. Wire the gfi with the INCOMING power feed into the LINE side of the gfi. Black to brass and white to silver.Pig tail the green/bare ground and run it into the green screw.

    Then from that gfi come off the LOAD side into your new plug with the blk to brass screw and the white to silver. Green once again pigtailed and connected to the green screw. Some of that old wire will have to go since you don't have the extra switches etc..

    Also trace it back to the panel and CUT THE breaker. Also note how many amps the breaker is?> Hopefully it is 20. You said it was for an in ground pool? What was it feeding? Just this box? Look and see on the breaker how many AMPS it is.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #9

    May 23, 2008, 05:58 PM
    I have some questions:
    1. When you say you have two "lines" coming-in, do you mean you have two circuits--a breaker controlling each circuit
    2. Where is your box located. Example: On the house or remote from the house
    3. Describe your current wires coming in. Example: is it a cable, or individual conductors. Also, if it's a cable-what color is the outter jacket
    rsrcwhite's Avatar
    rsrcwhite Posts: 16, Reputation: 1
    New Member
     
    #10

    May 24, 2008, 05:10 AM
    Washington... I have 1 circuit breaker... the box is 30 feet from the house. It comes up from the ground encased in a metal conduit. Two lines come into the box. I'm just trying to figure out how to utilize those 2 lines .Why would it have 2 lines coming up?
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #11

    May 24, 2008, 08:12 PM
    Quote Originally Posted by rsrcwhite
    washington....I have 1 circuit breaker...the box is 30 feet from the house. It comes up from the ground encased in a metal conduit. Two lines come into the box. I'm just trying to figure out how to utilize those 2 lines .Why would it have 2 lines coming up?
    If the wires are romex, then this a code violation. Yet, if you have THWN conductors installed, then what Mr. 500 suggested will work.

    Also, If I where you-after isolating the in-coming power-I would try and find out where the second pair (white and black) of conductors are coming from. I'm almost certain the second set of conductors are coming from the remote receptacle being switched. If so, you can wire the recpetacles to have constant power.

    Hope this helps!

    Write back if you need more help!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electric Heat & astronomical electric bills [ 3 Answers ]

We just moved into a new home with a Goodman. We are receiving astronomical electric bills. Our previous home was all electric and we didn't have this problem. We called back the contractor and they didn't find anything wrong. I have since found that the thermostat was set to "Comfort" for the...

Electric Heat & astronomical electric bills [ 1 Answers ]

We just moved into a new home with a Goodman. We are receiving astronomical electric bills. Our previous home was all electric and we didn't have this problem. We called back the contractor and they didn't find anything wrong. I have since found that the thermostat was set to "Comfort" for the...

Electric Force and Electric Field? [ 1 Answers ]

Hello, Can some one explain to me briefly what's the different between electric force and electric field? I am having trouble to make them clear to myself. Thanks you so much. Jack

Die-electric? [ 1 Answers ]

Does the code require die-electric unions for a gas water heater? 30 gallon tall . Oh sorry... I'm in columbus Ohio.

Gas Vs. Electric [ 12 Answers ]

I am terrible with engines so I was considering getting all electric Lawn equipment. What do you think I would be sacrificing ? I have a zero Lot line so I don't have that much to cut and Some of the equipment is wireless.


View more questions Search