    208V VS. 240V power
    Hello,

    Just want a clarification: 208v power comes from a wye connection(ie two line wires) does 240 come from a delta connection? Please explain

    Regards,

    l. fudge
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    May 22, 2008, 07:19 AM
    208/277 is typical 3 phase Y connected loads. 277 is used for lighting.

    Note that 208 is sqrt(3) *120.

    240 is typically a delta connection, but it's also residential "single phase"

    Remember that Y-Delta and Dela-Y transformations may be done using just a transformer.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    May 22, 2008, 01:41 PM
    Actually 277/480v is a typical Y 3-phase system. There is NO such thing as 208/277v 3-phase. Not in the US that I know of at least.
    120/208v is also a Y 3-phase system.

    120/240v 3-phase is Delta, with Line to neutral voltages of; 120, 208, 120. All line to line is 240v.
    pelle's Avatar
    pelle Posts: 96, Reputation: 0
    Junior Member
     
    #4

    May 22, 2008, 02:02 PM
    Stan you are correct, In my area voltages are 120/240, 120/208, 240delta, 480 delta, and 277/480.. Some of these voltages will come in 3 or 4 wire entrances.. 120/208 is made off 3 pots (transformers) using 2 legs. This is common in large apt bldgs and in commercial areas.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    May 22, 2008, 02:13 PM
    We had 120 sf, 277 sf (I think), 208 3 ph, 480 3 ph as built.

    But there were transformers put in place to yield some odd voltages like 380/3 phase and even some 240 V single phase. And there was one odd japanease piece of equipment that needed 100 V single phase.

    In that building all sorts of power was available.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Convert 208v to 480v [ 2 Answers ]

We bought a 20kW UPS that is designed for 480V 3 phase. We are moving to a building that is only wired for 208V. Is there any way to convert 208 3phase to 480 volt 3 phase or will we need to scrap the UPS?

240V space heater to 208V supply [ 1 Answers ]

I purchased a used construction 240V space heater (4.8KW) 12/2 cabtire wiring (rated 20A). Can I connect this to a 208V supply or must I re-size any items in the space heater

208v 3-Phase [ 1 Answers ]

Hello, We have a 208v 3-phase panel in our server room filled with 20amp circuits. We would like to change them to 30amp circuit that goes to the twist lock circuits so we can plug in bigger equipment. If all possible. What I can’t figure out is how many 30-amp circuits we can get in the 208v...

Can 208v be a substitution for 240v? [ 3 Answers ]

I've got a true 3ph 100A service and a 240v Cold Saw (for cutting steel). Can I rewire this saw for use in my 208v service? Obviously if I just grab 2 hots and the N I'll only get 208 across the poles and 120 at each leg, so I would assume that I would lose efficiency at the very least. But can...

480v Stepped Down To 120/208v [ 10 Answers ]

If I have a 600A 480v service and I step in down to 120/208, will I have an increase of available amperes at the lower voltage? Or will the amperage remain the same no matter how I change the voltage? Thanks


View more questions Search