Senior Member
|
|
May 20, 2008, 02:35 PM
|
|
Backwire receptacles
Anybody know if it's possible to get electrical receptacles for a 20 amp circuit that are backwired to accept 20 gauge wire? All I ever see is 15 amp size. They are so simple and quick. I want to add a new line and outlets in the kitchen so we can use the coffeemaker, microwave and toaster all at the same time without tripping the breaker. :confused:I am putting the GFCI in the breaker box.
|
|
 |
Electrical & Lighting Expert
|
|
May 20, 2008, 03:56 PM
|
|
You CAN use 15A receptacles on a 20A circuit.
I assume you mean "quickwire" as opposed to back wire. I also assume you mean 12 gauge wire as opposed to 20 gauge.
If you mean quick wire then DO NOT bother. They are completely NOT worth the slight savings in time. They are notorious for failing prematurely.
Besides, they do not make them for #12 wire any more as it has been illegal to use quickwire for 20A circuits for many years now.
|
|
 |
Uber Member
|
|
May 20, 2008, 03:57 PM
|
|
You DON'T want to backwire your recepticles, ESPECIALLY Heavy Loads.
They are a main source of many problems. It is Lazy(easy).
If for some reason you feel you must, and if it is allowed, Pigtail so if a problem occurs, it only affects that outlet. The Neutral MUST be Pigtailed(Can't have a white plugged in hole, and another white in another hole, in same recepticle).
I wouldn't, and don't do it.
|
|
 |
Senior Member
|
|
May 20, 2008, 09:54 PM
|
|
 Originally Posted by stanfortyman
You CAN use 15A receptacles on a 20A circuit.
I assume you mean "quickwire" as opposed to back wire. I also assume you mean 12 gauge wire as opposed to 20 gauge.
If you mean quick wire then DO NOT bother. They are completely NOT worth the slight savings in time. They are notorious for failing prematurely.
Besides, they do not make them for #12 wire any more as it has been illegal to use quickwire for 20A circuits for many years now.
I agree 100% with the above !
|
|
 |
Senior Member
|
|
May 20, 2008, 10:20 PM
|
|
The Neutral MUST be Pigtailed(Can't have a white plugged in hole, and another white in another hole, in same recepticle).
Sorry Strat, but this not fully true.
|
|
 |
Uber Member
|
|
May 21, 2008, 06:44 AM
|
|
Washington, what part?
|
|
 |
Uber Member
|
|
May 21, 2008, 07:41 AM
|
|
Bottom line. Don't do it. It's just a lazy way out. The connections in the back must be specified for a specific gage wire. The friction connections are not as reliable.
I think what people are getting at is that if you really want to friction fit the conductors, it's nicet to pigtail the neutral which hopefully will avoid "open neutrals" at a later point in time.
Pigtailing both neutral and hot is In my opinion, a better way to go.
|
|
 |
Senior Member
|
|
May 21, 2008, 09:36 AM
|
|
 Originally Posted by Stratmando
Washington, what part?
This part:
The Neutral MUST be Pigtailed(Can't have a white plugged in hole, and another white in another hole, in same recepticle).
Check your code book. Hint: The OP did not mention a multi-circuit
Per UL, back--stab (not srew terminal receptacles with back-stabs) receptacles are not allowed to accept 12 gauge wire--which limits the ampacity serving that device.
Yet, what do I know
:D
|
|
 |
Uber Member
|
|
May 21, 2008, 10:30 AM
|
|
Washington, your right, Op didn't say Multi circuit, I didn't want to explain "Multicircuit"and would prefer to err on the side of safety.
If you don't pigtail your neutrals and you feel fine with that method go for it.
Years ago I worked with an Inspector that felt backstabbing was as good as around the screw. I always wanted to have 2 recepticles in series, 1 backstabbed and 1 around screw and apply about 40 Amps and see which blows open. I never did, he passed on, I really believe the backstabbed would blow open. Beliving is different that proving out, so who knows?
|
|
 |
Uber Member
|
|
May 21, 2008, 11:17 AM
|
|
Everyone here will tell you, backwiring sucks.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Receptacles near bath tub
[ 18 Answers ]
My wife and I are converting half of a bedroom into a bathroom and a walk-in closet.
There is a electrical receptacle across from the future location of the bathtub -- about 3 feet from where the water will be.
Is this safe? (i.e. is this acceptable within the electrical code?)
I...
Receptacles not working
[ 1 Answers ]
I hope that someone will be able to provide some additional steps to take to investigate the cause of my problem.
My house was built in the 1950's, and has two panel boxes, one fuse box for the original, older portion of the house and a circuit breaker box for the addition and remodeled portion....
Gfic receptacles
[ 1 Answers ]
My electrician installed 1 gfic receptacle in my bathroom to cover 2 outlets and 2 gfic receptacles in my kitchen to cover 4 outlets. The person buying my coop doesn't believe that all these outlets are covered from what I had installed. Could you please explain how all the outlets are covered by...
15 or 20 amp receptacles?
[ 6 Answers ]
I had my electric service upgraded 18 years ago and had the electrician install two GFCI's,
One for the bathroom and one for the kitchen. They are on separate circuits by themselves. They are each on a 20 amp breaker with 12 gauge wire and the GFCI's are rated 15 amp with 20 amp feed through.
My...
Basement receptacles
[ 4 Answers ]
Hi, I want to put four receptacles in my basement, its an unfinished basement and I'll put in a
GFCI plug. My question is this: do I bond the metal boxes and Im not sure if I am supposed to ground the plugs that are fed off the GFCI? And I do ground the GFCI in the panel don't I? Thanks
View more questions
Search
|