Depends. Is this cable subject to damage for this 4-5 feet?
I thought it depended on if it the wire were exposed or in the wall. :eek:
Here is a quick picture--
First off, #8NM cable is good for 40 amps, NOT 50
My bad. You are 100% right. I was thinking of THHN #8
__________________________________________________ ________________
I am now thinking my best bet is to run another line from the main panel to a new sub-panel:rolleyes:
If I should decide to do this here are a couple of questions--
Conditions and Uses--
1) This will be run from main box to sub-panel thru an attic for a distance of 130-140 feet.
2) I would think THHN in conduit would be wise??? Not sure about NM Cable
3) Tempature in the attic would get warm as the location is Southern California--Thus, summer time outside temperature can reach 100, attic would be much higher than this.
4) The panel will be used for a wood work shop(
biggest motor is 3hp). Currently, the most I can see on at one time would be--
- 6- 8' fluorescent shop light at 1.25 amps each~Total 7.5 amps--120 Volts Continuos
- 1- Small Window AC or Wall Heater~Total 15 amps-120 Volts Continuous
- 1-Shop Dust Collector--Total 12 amps--220 Volts Not Continuous
- 1-Table Saw--Total 18 amps--220 Volts Not Continuous
Given the above information I would think I would want to run four #6 THHN wire--2 hots, 1 neutral, and 1 ground. For conduit I would use EMT 3/4".
I would think a 50amp sub-panel should handle this load fine.
Questions-->
Is my above thinking correct? 50 amps sub-panel with #6 THHN wire.
I am unsure on the conduit--I have always used EMT, but my runs are not 140 feet. The size, I would think required would be 1" either PVC or EMT? Any suggestion on which one to use?
Am I forgetting anything?
Thank you stanfortyman, Washington1, donf for your feedback. It nice to get some feedback before starting something. This way you don't find out later you left something out.:eek: I have been there before and it really sucks.