-   -   Sizing the kva for TRANSFORMERS (https://www.askmehelpdesk.com/showthread.php?t=97738)

  • Jun 1, 2007, 06:05 PM
    MRCHAD
    Sizing the kva for TRANSFORMERS
    What Would Be The Right Size Transformer.

    Power Coming In Would Be Single Phase 480

    Output Is 120v , About 4.2a

    I Figure About 1kva Would Be Plenty
  • Jun 2, 2007, 03:21 AM
    tkrussell
    Since VA (AC Power) is volts times amps:
    120 VAC X 4.2 Amps= 504 VA
    So the 1.0 KVA xfer is almost double what is needed, offering plenty to spare, if the load is resistive. If the load is inductive, such as a motor, it is just about the correct size.
  • Jun 7, 2007, 03:30 PM
    nielseno
    Quote:

    Originally Posted by MRCHAD
    What Would Be The Right Size Transformer.

    Power Coming In Would Be Single Phase 480

    Output Is 120v , About 4.2a

    I Figure About 1kva Would Be Plenty

    I think you'll probably be OK. I think you just need to multiply your 120*4.2 and w/ a 1 KVA rated supply you would have a safety factor of 2.