Originally Posted by DeeBetee
Hi All,
Ive done a lot of research on here but am yet to find an answer specific to my problem so any ideas would be greatly appreciated.
I have recently installed a Honeywell T8624D to operate my Carrier Heating / Cooling system. THis thermostat is replacing a manual slider-type unit.
I have 4 wires to my tansformer as follows:
Red - Hot
Green - Fan
White - Heat
Black - Cool
I have wired the unit in the following manner with *some* success:
Red - Rc-Rh (jumpered)
Green - G
White - W1
Black - C
My research told me that Black was supposed to go to Y1 to operate the Cooling compressor but if I do that I lose all power to the thermostats LCD as I understand the C terminal must be wired to close the circuit.
So basically I am at a point where my heating and fan work fine, but I cannot get the Cooling Unit to start. I have tried a few suggestions of Jumpering W1 to Y1 and have not had any success either.
Again, any help would be most appreciated. Cheers.