Originally Posted by JackT
You must be referring to the low voltage fuse and not the line voltage fuse (I'm assuming low voltage as when it blows, I have no 24V power to the thermostat). If the 5 amp fuse only blows when you switch it over to the cooling mode, you probably have a problem with the condensing unit. Check the small 24 volt wires going outside to the unit. If they appear to be in good condition you probably have a problem inside the condensing unit. Depending on the make and model, it could be the coil on the contactor, time delay relay, or the circuit board itself or the reversing valve coil. (if its a heat pump)