Relocating underground conduit and meter base
I am putting a small addition on my house and have to move the service entrance underground conduit and meter base from one wall, around an outside corner to an adjacent wall. The meter base is about 2 feet from the corner of the two walls and I am hoping to dig down to the 3" schedule 40 conduit for a horizontal length of perhaps 15 to 20 feet, "bend" the conduit up and move it over to the other wall and drop it back down. It will end up about 3' from the same corner but on adjacent wall. I will not move the interior breaker box. 200 Amp. Uses SER, 2 ea 4/0 & 1 ea 2/0 AL. (I am assuming the service entry cable is in conduit all the way to the pad mounted transformer).
I am hoping not to cut the schedule 40 and not even disconnect the conduit from the meter base. (The power company will shut power off during this maneuver). I don't know how much horizontal distance it will take to uncover the conduit enough to "bend" it enough to make the change.
Question is: can I use individual XHHW-2 conductors inside rather than the SER cable between the meter base and breaker box? I have to reroute the cable inside and have to turn a corner through 2x6's. I don't know whether I can form the SER cable around the corner. I would have a much better chance forming the conductors one at a time through the studs. I would use nail plates for protection. I plan to sheetrock over the two adjacent walls...
I don't understand the difference between SEU and SER. And since the total length of the cabling will be perhaps 10 feet, would it make sense to use 3 ea 2/0 copper conductors instead of the aluminum wire? --- perhaps I could purchase 30 foot of copper conductor more easily than 10' of aluminum 2 conductor and ground SER/SEU cable.
Thanks for the advice!
Frank