    taterbradley
    Thermostat Wiring
    I am having similar thermostat problem as krich22774 had on 4/16. I installed the Honeywell RTH230B thermostat during the winter and the heat worked fine. Now when I turn on the A/C nothing happens.

    I have 5 wires coming from the wall. I started with the following setup:

    Rh-Red
    Rc-Blue
    W-W
    Y-Y
    G-G

    After switching to the following I got A/C working correctly, but no heat.

    Rh-Blue
    Rc-Red
    W-W
    Y-Y
    G-G

    After switching to the following both A/C and Furnace turned on.

    Rh-Blue
    Rc-Jumper
    W-W
    Y-Y
    G-G

    After switching to the following I got nothing to work.

    Rh-Blue
    Rc-Jumper
    W-W
    Y-nothing
    G-G

    I have a Bryant 350AAV furnace and a Bryant 561CJ030-E outside A/C unit. Any help or suggestions would be greatly appreciated. Thanks.
  • May 2, 2007, 07:20 PM
    hvacservicetech_07
    RC-RH... install jumper and red wire

    W-W

    G-G

    Y-Y

    Leave the blue unhooked
  • May 2, 2007, 07:24 PM
    hvacservicetech_07
    Jumper needs to be between RH and RC and hook your red wire to one of the two
  • May 5, 2007, 09:01 AM
    taterbradley
    This worked. Thanks a lot.
  • May 5, 2007, 09:09 AM
    hvacservicetech_07
    Not a preoblem! If you would, I would appreciate it if you rated me by clicking the button below