Maximum distances from the waste line vent
	
	
		Are there generally code requirements for waste line runs in regards to how far the waste line runs from the roof vent?  For example, if I convert an existing bedroom into a bathroom and the toilet is say 10 feet away from the waste line roof vent, is that going to be a problem?
	 
	
	
	
		Maximum distances from the waste line vent
	
	
		
	Quote:
	
		
		
			
				Originally Posted by tegelert
				
			
			Are there generally code requirements for waste line runs in regards to how far the waste line runs from the roof vent?  For example, if I convert an existing bedroom into a bathroom and the toilet is say 10 feet away from the waste line roof vent, is that going to be a problem?
			
		
	 
 
Let me quote from Table 1409.3 of the Standard Plumbing Code titled    "Distance of Fixture Trap from Vent",
 
Size of Fixture Drain                  Distance Trap to Vent
1 1/4"   -------------------        2 ft 6 in.
1 1/2"    ------------------        3ft.  6 in.
2" ------------------------        5 ft  0 in.
3" ------------------------        6 ft  0 in.
4" ------------------------        10 ft  0.in.
	 
	
	
	
		Can runs be longer using loop vent?? 
	
	
		If I utilize an overhead loop vent from the trap back to the main stack, can the waste-line runs be longer than than what's specified in the Standard Plumbing Code?
If so, what are the rules in that case?
Thanks!