  • Mar 18, 2017, 09:31 AM
    tompetschauer
    BRT-45 garage heater
    My heater will go through start up. Induction motor on, burner on, circulating fan on. It will run for a minute or two and then burner will cut out. LED light blinks 4 time, indicating limit or rollout switch is open. How can I trouble shoot what is wrong?

    Thank you,

    Tom
  • Mar 18, 2017, 11:54 AM
    ma0641
    Look for the rollout switch and try a reset, most have a red reset button. Should be on the schematic. If it does it again, you may have a dirty filter, blocked flue, snow, bird nest etc. If it is a condensing heater, look for water or ice in the intake or exhaust pipe.
  • Mar 19, 2017, 11:57 AM
    tompetschauer
    Thanks for the tips. The heater appeared to kick out on hi limit. After checking other things, I took the circulating fan out and clean and lubed it. That seemed to fix the problem. Apparently the fan was running slow enough to let the plenum overheat.