Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Low voltage fuse blowing on ac controlboard (https://www.askmehelpdesk.com/showthread.php?t=829762)

  • Jan 8, 2017, 01:57 PM
    lucian22
    Low voltage fuse blowing on ac controlboard
    My thermostat went blank so I replaced it. Turned on the heat and nothing, checked the 5 amp fuse and it was blown. The fan turns on until I try to turn on the heat. I disconnected the low voltage going outside and the problem remains. I can turn on the heater by jumping the wires on the control board. Help please!!
  • Jan 9, 2017, 12:42 PM
    Stratmando
    Not sure where you are jumping? Since it doesn't do it on cool, wiring to compressor appears OK. The Heat relay may be shorted. Remove heat wire in air handler, try again, if it blows, it is more likely in thermostat wiring. Good Luck, keep us updated
  • Jan 15, 2017, 09:15 AM
    lucian22
    I found a blown 1k ohm resistor. The heater works when I disconnect the blue wire, not trusting that though since it is the neutral.
  • Jan 15, 2017, 11:06 AM
    ma0641
    Where are you located? Neutral for what? If for the main 120 VAC power, would not work with neutral disconnected and most likely not blue since
    NEC code requires white or gray. In UK and most of Europe, blue is neutral.

  • All times are GMT -7. The time now is 09:12 AM.