Originally Posted by shuntripper
you may need another electrician. How would he compensate for voltage drop on a very long circuit? putting 20A wire on a 15A CB is not a problem and is actually REQUIRED in circumstances like the above. Putting a 20A receptacle on a 15A circuit is no problem either, What IS a problem though, is a lower rated wire on a higher rated CB . The NEC states that 14awg wire is not to be on a CB or fuse rated more than 15A, 12awg not more than a 20A CB, and 10awg not more than a 30A CB.:confused: But why do you want 15A Circuit Breakers anyway when you are running 12awg wire? The only reason to use a 15A breaker is because you have 14awg wire and the Code says you have to, there can't be much of a price diff between the CBs.