I have a 80amp breaker box. I'm wanting to but 4 breakers in it. A 30--20-- and to 15 breakers. What size wire do I use from the meter pan to the breaker box. They are both on a pole
![]() |
I have a 80amp breaker box. I'm wanting to but 4 breakers in it. A 30--20-- and to 15 breakers. What size wire do I use from the meter pan to the breaker box. They are both on a pole
Wire Size Calculator
Does this help?
You are leaving an awful amount of critical information out of this question. Is this installation for a motor home or mobile home?
Meter pans are usually owned by the POCO, have you contacted them as to where they want the meter and pan?
Have you completed a load study to make sure that:
1) 80 Amps is sufficient and (2) You have sized and planned the branch-circuits correctly?
Are all of the circuits going to be 100% loaded, and all of them on at the same time carrying the full load?
If this is for a residence, than 80 Amps is not a sufficient load. 100 Amps is the minimum.
I assume this is a temp construction pole. We could surmise about everything but until we hear back??