  • Apr 14, 2016, 08:01 AM
    service0063
    50A plug vs. 40A breaker/service
    We manufacture laboratory equipment. This unit is rated for maximum 40A.

    We ask the customer to install a 40A breaker in the circuit. The plug installed is a L6-50. Why is the plug not rated for 40A like the breaker?
  • Apr 14, 2016, 11:57 AM
    ebaines
    This sounds like a homework question to me. Think about it - if a fault occurs would you rather have the circuit breaker tripping or the plug over-heat?
  • Apr 14, 2016, 02:22 PM
    ma0641
    Because a NEMA L6-50 is rated for 50 Amps. It works fine with a 40 Amp breaker. That is what determines the maximum current, not the plug. There is no NEMA L6-40, only 30 and 50 and using a 30 would be a code violation.