  • Apr 9, 2016, 07:24 AM
    Scourt
    Water collecting in inducer blower fan.
    We have a Armstrong Air Ultra 5 Enhanced 95V furnace and water keeps collecting in this fan housing of thr lnducer blower. Which maker the inducer motor run hot and the furnace shuts down before the house warms up to temp.
  • Apr 9, 2016, 09:14 AM
    ma0641
    Sounds like condensation from the vent is falling back down into the inducer. This is aggravated with cold weather and long piping runs. You may also have a sag in the horizontal vent and it allows water to run back. I believe the unit is shutting down because of pressure buildup in the vent and the pressure switch is not closing.