  • Dec 12, 2015, 02:15 AM
    Riles530
    Rheem gas furnace RGDE 07NMAGR, fan comes on but nothing else
    If I turn the power off and restart the unit, the fan comes on but I don't see or hear the igniter and I'm not able to tell if the gas is coming on either, I assume that is a safety feature
  • Dec 12, 2015, 04:07 AM
    parttime
    Hi Riles and welcome, the fan you hear running is the inducer fan, it should start and activate a pressure switch. Do you have good airflow outside at the exhaust? Make sure the pipe is clear. If that checks out I would suspect the pressure switch is bad. Good luck
  • Dec 12, 2015, 09:19 AM
    ma0641
    What fan? Air handler or inducer? Are there any codes shown on the board?
  • Dec 12, 2015, 10:18 AM
    Riles530
    this is a pretty old unit, there are no trouble codes or display
  • Dec 12, 2015, 10:28 AM
    Riles530
    Quote:

    Originally Posted by parttime View Post
    Hi Riles and welcome, the fan you hear running is the inducer fan, it should start and activate a pressure switch. Do you have good airflow outside at the exhaust? Make sure the pipe is clear. If that checks out I would suspect the pressure switch is bad. Good luck

    thank you, is there a procedure for checking the pressure switch with a multi-meter, or what values should I be looking for? voltage or resistance?
  • Dec 12, 2015, 10:56 AM
    parttime
    Hi again Riles, yes there is a procedure for checking the pressure switch, but it involves special tools that are rather expensive. If it was mine and I was sure the inducer fan was blowing strong and the exhaust was clear I would turn off the furnace power, disconnecting the two wires going to the pressure switch and temporarily connect them together, set the thermostat for heat, then put the power in and see if it fires up. If it does then I would kill power and replace the switch. This is something I would do to trouble shoot the furnace and I would never​ run it like this. Good luck
  • Dec 12, 2015, 11:54 AM
    Riles530
    I just finished with the pressure switch continuity test and it appears that the circuit remains open weather the induction fan is on or off, so now to locate one on a Saturday, thank you parttime
  • Dec 12, 2015, 12:04 PM
    Riles530
    I just cut the power and connected the 2 pressure switch wires and when I restored power and set the thermostat for heat and nothing happened, same as before, induction fan only, not sure what to make of it now
  • Dec 12, 2015, 12:30 PM
    parttime
    Rile, did you block the door switch when you did the test?
  • Dec 12, 2015, 01:52 PM
    ma0641
    According to the Rheem website, this series has spark ignition and a "Diagnostic control board". Are you sure there is no LED on the control board. Did you look for a fuse on the board. There are roll out switches and an upper limit safety. Download the manual from Rheem and look at the schematic.

    Rheem Furnace User Manuals Download - ManualsLib
  • Dec 12, 2015, 02:34 PM
    Riles530
    yes sir, door switch accounted for
  • Dec 12, 2015, 02:45 PM
    parttime
    Riles can you post a picture, does one of the panels have a schematic?
  • Dec 12, 2015, 02:49 PM
    Riles530
    my particular model is not listed on the rheem site or manualslib, it's been kicking my tail without anything to refer to, you guys are awesome but a picture is worth a thousand words and electrical is not my strong suit
  • Dec 12, 2015, 06:10 PM
    Riles530
    3 Attachment(s)
    Attachment 48046Attachment 48047Attachment 48048

    I hope this works
  • Dec 13, 2015, 01:05 AM
    Riles530
    I found an LED on the hot surface ignition module but overlooked it because it doesn't come on during regular operation, when there is a command for heat, I can hear the module click once and the inducer fan runs but the LED never lights up, there is 24v to the module
  • Dec 13, 2015, 06:12 AM
    parttime
    Hi again Riles, the pictures didn't do much for me and my old eyesight, sorry. Maybe someone else can make more of it.
  • Dec 13, 2015, 08:45 AM
    ma0641
    Yep, sure looks old but, I knew there was a board somewhere with an inducer and a pressure switch. Looking at your pictures: That is a normally open pressure switch and will close on negative pressure from the inducer. The little rectangular black plate with 2 wires is the high limit. Make sure there is 24 VAC across it when calling for heat. Looks like a roll out safety to the left of the gas valve. They are resettable if tripped, small toggle switch. Check for a fuse on the control board, 5 amp car type.
  • Dec 13, 2015, 11:53 AM
    Riles530
    1 Attachment(s)
    there is 26v across the high limit switch when calling for heat, is too much a problem? and as far as the roll out safety(pictured) I can't locate a toggle but the top has a loose kind of red button deal on itAttachment 48049
  • Dec 13, 2015, 12:24 PM
    parttime
    Riles you can test the rollout switch using your meter, test for continuity.
  • Dec 13, 2015, 12:57 PM
    Riles530
    it tested o.k.