  • Nov 29, 2015, 02:29 PM
    brundlefly4
    While replacing an old main lug, noticed a/c feed was hooked to a 30 amp c.b. with 2s
    sorry. while replacing main lug, noticed a/c unit was connected to a 30 amp c/b with 2 term.screws but hooked to same bus bar connector. is that even possible? unit is a 208/230 comp, 208/230 fan. panel was an old fed. pacific.
  • Nov 29, 2015, 02:48 PM
    ma0641
    Every other slot goes back to the other side. It may look like a 240 is connected to one side but it isn't, otherwise you'd never get 240, only 120. They are 120 VAC phased at 180 degrees opposite each other, switching 60 times a second.
  • Nov 29, 2015, 03:02 PM
    brundlefly4
    ma0641. I realize that and I know that it's connected to one slot , not 2. that's why I'm so dumbfounded. I'm guessing that's f.p.'s style of a double wire single pole c.b.
  • Nov 29, 2015, 05:38 PM
    hkstroud
    Show us a photo of this breaker and panel.
  • Nov 29, 2015, 08:10 PM
    ma0641
    FP panels are pretty much gone today. With all the past issues and lawsuits, why not change it?

    Is My Electrical Panel Safe? - Important Information About Federal Pacific Electric, Zinsco and Outdated Electric Panel Boxes
  • Nov 29, 2015, 08:26 PM
    brundlefly4
    Trying to send picture but won't upload. Don't know what I'm doing wrong. Will try again tomorrow after frustration calms down.
  • Nov 30, 2015, 06:19 AM
    hkstroud
    Load photo to computer. If necessary convert file to JPEG format. If necessary reduce size of photo to reasonable size. When photo is to big it makes post hard to read post.

    Make your post, click on "Go Advanced" below Quick Answer box.
    Scroll down and click on "Manage Attachments".
    Click on Add Files,
    Find and open file,
    Click on "Done",
    Click Submit.
  • Nov 30, 2015, 07:12 AM
    donf
    Typically FPE used a "Split Bus" panelboard, at least that's what I had.

    The high amp breakers were in the top half of the split and the lower amp breakers were in the bottom split. For example a 60 Amp A/C breaker would be a dual breaker connecting to slots one and two. Slot one would be one 120 Volt phase and Slot two would be the other 120 phase.
  • Dec 1, 2015, 09:08 PM
    brundlefly4
    C:\Users\Owner\Pictures\2015-12-01\New folder\537.JPG Every time I've tried to add a picture , the pic comes up on computer with the file name but when I add the file and push "done" this is what I get. Guess I'll have to get my kid involved.
  • Dec 2, 2015, 05:56 AM
    hkstroud
    After you click "Add files", then click "Select Files" and file comes up, are you clicking on "Open" before clicking "Done"?
  • Dec 2, 2015, 10:32 AM
    brundlefly4
    Yes. I'm not going to let this beat me. Try again after work
  • Dec 2, 2015, 12:48 PM
    hkstroud
    I have sent you a private message.