    Boiler Drip
    I have a Carrier BW9 condensing hot water boiler. The concentric intake/exhaust pipe was just lengthened from 10 feet to approx. 40 feet. I now have a drip from the 3 inch hose at the bottom of the boiler that connects to the PVC exhaust. The clamps may have loosened from new installation. My question is " Should there be any condensation there at all or was it a mistake to lengthen the exhaust? Thanks
  • Aug 29, 2015, 08:09 AM
    ma0641
    A condensing unit produces water. In a short length it probably heats up enough to evaporate the water. With a 40' length, probably not. The pipe is PVC?