Feeding 100amp panel
![]() |
Feeding 100amp panel
Coming out from my house panel to new building
We need more information.
Is the panelboard in a remote structure? How far apart are the two panelboard's?
Jerry please keep you questions and responses in the same thread.
To drive 100 amp 200 feet underground, will take a four wire aluminum 2/0 AWG. Also, neutral and ground have to be isolated at the remote panelboard and the remote building must have its own grounding system.
M.B.
Thanks for catching my typo. Don