  • Nov 19, 2014, 11:49 AM
    markwells111
    Why does my central heating unit stay on
    Why does my central heating unit stay? / I changed the thermostat on the wall and put a new one in. the blower motor no longer runs. The heating element stays on.
  • Nov 19, 2014, 03:44 PM
    Grady White
    Is this furnace electric, gas, or oil?
  • Nov 19, 2014, 09:37 PM
    markwells111
    Electric
  • Nov 20, 2014, 10:06 AM
    markwells111
    Quote:

    Originally Posted by Grady White View Post
    Is this furnace electric, gas, or oil?

    The unit is all electric
  • Nov 20, 2014, 10:12 AM
    bitters
    What is the make and model number?
  • Nov 20, 2014, 02:38 PM
    markwells111
    Nordyne intertherm model E2EB -15HA 1/3 horse power 4 speed 4 ton.

    ]Nordyne intertherm model E2EB -15HA 1/3 horse power 4 speed 4 ton.[/QUOTE]
  • Nov 20, 2014, 03:55 PM
    bitters
    1 Attachment(s)
    Quote:

    Originally Posted by markwells111 View Post
    Nordyne intertherm model E2EB -15HA 1/3 horse power 4 speed 4 ton.

    ]Nordyne intertherm model E2EB -15HA 1/3 horse power 4 speed 4 ton.

    [/QUOTE]

    Look's like the fan relay is bad (IFR2).
  • Nov 20, 2014, 07:06 PM
    Grady White
    The thermostat may have to be configured for electric heat. Refer to the installation booklet which came with the new thermostat.
  • Nov 22, 2014, 11:04 AM
    markwells111
    Quote:

    Originally Posted by Grady White View Post
    The thermostat may have to be configured for electric heat. Refer to the installation booklet which came with the new thermostat.

    Grady I replaced with the same type. I brought both at the same time years ago. Do you think maybe the 3 pole sequencer is bad? Is it part of the fan relay?
  • Nov 22, 2014, 12:09 PM
    bitters
    Your unit doesn't have a sequencer. The contactor pulls both heat strips in at the same time. If the heating elements are coming on the contactor is good. I would replace the relay (IFR2).

    With the fan not running the limit switch should shut off the element's.