  • Nov 3, 2014, 02:58 PM
    Barnrat1113
    Electronic ignitor stays lit all the time on Goodman GMP075-4
    My electronic ignitor stays on all the time on my Goodman GMP075-4. Even when the a/c is running the ignitor glows hot. As long as there is power to the unit it stays on. Before I change the circuit board could it be anything else?
  • Nov 3, 2014, 03:54 PM
    bitters
    Sounds like the board is bad. Does it go off when there is flames?
  • Nov 3, 2014, 08:14 PM
    Barnrat1113
    It won't even fire up. The a/c works fine. But nothing happens when the thermostat calls for heat. Except the electronic ignitor glowing all the time.
  • Nov 4, 2014, 10:04 AM
    bitters
    If the combustion blower and the furnace blower are not running, then the hot surface ignitor relay is stuck. Tap the relays on the board and see what happens.