Is a small leak in a water well line acceptable? Pressure tank is losing pressure.
Thanks so much in advance for your help. This has been a trial and error learning experience. Your answers to other people's questions really helped us in getting this far!
Troubleshootin and repairs we've already done:
Our pressure tank was losing pressure rapidly. Cycling every 7 minutes with no water usage.
1. We closed off the valve to the house. The cycling still occurred, so leak was on the well side.
2. We dug down to the pitless adaptor and put in a check valve by the well head. The cycling still occurred, so leak was in the well line, and not in the well.
3. We dug a couple holes, didn't find the leak, then finally called a leak detector guy, who pressurized the well line with helium, and he isolated the leak to an elbow in the PVC plastic. This cost $600, but was way better than continuing to dig up holes (This is the Rocky Mountains!! ) We dug that up, found the leak squirting out, and fixed it.
Current situation:
We then started the system, and there is still a small leak occurring. The pump now cycles every 4.5 hours (without usage), so there will be about 6 additional pump cycles / day, and about 40 gallons of water lost per day. The leak detector guy says this leak is so small that it will be very expensive to find it, and I should just keep an eye on it. We still have the holes open near the pitless adaptor, and at the repaired elbow, and a couple others, so I think it would be easier to find now when we can see exactly where the pipe is going. We've already had a light freeze, so I need to get this buried.
Should I just fill all the holes and monitor it, or should I have the leak detector guy come out and pay another $600 (or more? Not sure - how long it will take him, he says more expensive that the first).
Or any other suggestions? I've read about putting a check valve in near the pressure tank on other answers. This would prevent the pump from cycling, but wouldn't that also mask the leak problem, so I wouldn't know if it was getting worse?
Details of system:
We have a deep well, with a couple hundred feet of 1" PVC pipe buried about 6 feet deep. The pipe comes into the garage, goes into the pressure tank and then into the house. There are two manual shut off valves, one on each side of the pressure tank.