How many amps, at 400 volts, can I get from a 300 kva [ 480v/ 400v] transformer?
![]() |
How many amps, at 400 volts, can I get from a 300 kva [ 480v/ 400v] transformer?
This answer can vary depending on the type of load. Assuming a non-inductive load,(no large motors) then your answer would be 300kva/400volts output=750 amps. This is in an ideal situation. In reality you have a less then perfect energy transfer, the "standard" for industrial applications is usually to caclulate for a 60% efficiency or Power Factor(PF). In this case 300kva*.6PF =180000/400volts yields you approximatley 450 Amps.Quote:
Originally Posted by Nathonian
Hope This Helps,
Morrowrj
The expression Volt Amps of AC power, will include any power factor consideration on the circuit. A transformer rated in KVA will not need to be derated for any inductive or capacitive load.
Assuming this is a 3 phase transformer, due to the size and voltages involved, the amps available on the 400 volt secondary side is calculated:
300,000 VA / 400 volts * 1.73= 1297.5 or 1300 amps
Hmm, I normally work single phase... However it still seems like your calculation is off? Is it possible that the equation is KVa divided by the quantity of volts times 1.73 ?
300,000VA / (400 V * 1.73)
or
300,000Va / 692 = 433 Amps.
Please see here :Rex Power Magnetics - Home Page
Or here : How To Size Phase Transformers
Please let me know if I am missing something.
Morrowrj
Sorry I missed this, thought I would get subscribed just by answering.
You are right ,I can't believe I said that. The brackets mean to calc phase to phase voltage of 692, then divide.
Morrow is correct, the amps is 433.
Hello There
Sorry New, What Would Be The Right Size Transformer.
Power Coming In Would Be Single Phase 480
Output Is 120v , About 4.2a
I Figure About 1kva Would Be Plenty
Yes, I agree 1kva should be good. Did you check the links I referenced above?
Morrowrj