3-phase AC Panel Load Calc
Hello,
I am having trouble figuring out the attached AC panel power numbers. Looking at circuit 1, if P=VI, and P=1440, V=120, then I=12A, is that was why a 20A breaker was selected? Now to circuits 24/26 where a 2-pole 30A breaker was installed, P=2496 per leg, V=120 per leg, so I=20.8A per leg, is that why a 30A dual pole was used?
I am looking to install three (3) new 30A dual pole breakers in this panel and I am trying to run the numbers to see if it will be over loaded. Each breaker will be feeding a rectifier unit for a DC power plant. To get the VA power value on each leg do I just take the worst case scenario power draw of 30Ax120V to get 3600VA? Should I use the manufacturer's nominal current draw of 12-14A for the power calc instead? If you need me to provide more information please let me know. Thank you in advance for your time.
After I input the worse case scenario numbers, C-phase is slightly higher than A-B. Will this be an issue.Attachment 46376
-Guy