  • Jul 22, 2014, 08:36 AM
    tunatime
    Can I plug a 120/220 plug into a 30A-125/250 outlet and how?
    Hello,I have a Mig welder with a 220 plug on it.I have a dryer outlet, it's a Leviton 4 plug/wire 30A-125/250V.The plug on the welder is smaller than the outlet.I can plug welder into my 220 outlet that is used for my air conditioner butthat is located in my living room.The dryer outlet is in the basement in a ideal location.My question is, can I use some sort of an adapter that I could plugmy welder into and plug that into the 30A-125/250V. The manual for welder says you can install a 250v plug if needed.I was hoping to use a plug adapter if they make such a thing.Any help would be great and I'm sorry I don't know all the right terminology.
  • Jul 22, 2014, 05:31 PM
    ma0641
    If your welder is straight 240 VAC, you cannot use the 120/240 dryer outlet, you need a 240 VAC outlet. What does your MIG plug look like, 1 straight and 1 horizontal plus the ground?
  • Jul 23, 2014, 06:04 AM
    tunatime
    The plug on my MIG is a NEMA (6-50P) 2 straight and 1 ground 1 straight is bigger than the other. My outlet is a NEMA 14-30R.If I cannot find or use an adapter then would you recommend I change the outlet?I do not use the outlet for the dryer anymore.Thank you for your help!

    The plug on my MIG is a NEMA (6-50P) 2 straight and 1 ground 1 straight is bigger than the other. My outlet is a NEMA 14-30R.If I cannot find or use an adapter then would you recommend I change the outlet?I do not use the outlet for the dryer anymore.Thank you for your help![/QUOTE]
  • Jul 23, 2014, 11:45 AM
    ma0641
    The plug on the welder is a straight 240. Just change the outlet to match and use the 2 hots and a ground, not the neutral, just cap it off. I meant 2 horizontals but had a vision of a 20 Amp 120 outlet.
  • Jul 23, 2014, 01:05 PM
    Studs ad
    I don't know of any adaptors that will do what you are looking for, so an adaptor is probably out of the question.

    F.W.I.W.
    The 6-50P plug sounds like the typical 50 amp welder plug supplied with most 240 volt welders. That being the case the welder is probably rated at about 40-50 amps. If that is the case then the dryer wiring is legally too small and you shouldn't connect to it.

    If you plan on using the welder on a regular basis I would suggest putting the investment into getting the proper breaker and wire and receptacle to the place where you are doing your thing. It just makes sense. The next guy that owns your home may look at the plug you installed at your dryer and match his dryer cord to it not knowing the difference, and he would be out of compliance. Just not a good practice.( If the plug were located somewhere else where it wasn't obvious that it should be a dryer plug, it would not be an issue if the amperage etc. was correct for the wire size and breaker size). The location of the current receptacle would indicate to me that it should be a dryer- next to washing machine outlet, washer drain, dryer vent, laundry room etc.) The electrical part can work, but the application doesn't.

    If you are just going to use the welder on rare occasions then converting the dryer plug to the welder could be done providing your welder is rated 30 amps or less, but I don't recommend. You will have to know which wires to connect to your new plug. I can make a lot of things work in a pinch, but it has all been temporary and safe and necessary in the situation and returned to proper state at the first available opportunity. You don't meet that criteria, so my suggestion is to spend the $ and do it the way it should be. You will find the convenience well worth it in the long run if you don't have to run cords all over the place or change the plug out every time you want to use your welder, and you and others safety won't be compromised.