Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Cooktop 30 amp Breaker Consequences (https://www.askmehelpdesk.com/showthread.php?t=796804)

  • Jul 15, 2014, 03:52 PM
    MJS17
    Cooktop 30 amp Breaker Consequences
    I have wired a cooktop to a 30 amp breaker but the specs call for a 40 amp. What will happen?
  • Jul 15, 2014, 04:20 PM
    donf
    Do you mean apart from the electrical code violations?

    If the cooktop tries to draw the full 40 amps, the 30 amp breaker will trip.
  • Jul 15, 2014, 04:23 PM
    stanfortyman
    If the specs call for a 40A circuit why did you wire it to 30A?
  • Jul 15, 2014, 07:24 PM
    ma0641
    It will trip the breaker and you will not be able to use the unit.
  • Jul 16, 2014, 06:05 AM
    Missouri Bound
    Can you tell us how this happened? Was the wire already in place? Did you simply make a mistake? It's not going to hurt the appliance, but it will limit just how much of it you can use at once. The breaker tripping will get annoying enough for you to do it correctly.
  • Jul 17, 2014, 03:51 AM
    hfcarson
    have you tried it?
  • Jul 17, 2014, 04:50 AM
    smoothy
    I'm guessing they were trying to avoid spending the roughly $12 for the correct breaker or didn't find out what the requirements were before wiring the job and undersized everything.
  • Jul 17, 2014, 06:03 PM
    hkstroud
    Don't change that breaker unless you also change the wiring.
  • Jul 17, 2014, 06:07 PM
    smoothy
    Agreed... what size wire is in it now?