    Sewage removal
    Distance from pump to place check valve
  • Jun 8, 2014, 07:09 AM
    ma0641
    As close as possible. Otherwise, if you have to pull the pump you will have a lot of waste to deal with. Mine is 30" above the lid and offset to the side using a 45 elbow.
  • Jun 8, 2014, 08:09 AM
    massplumber2008
    Hi MP

    We usually install the check valve above the ejector pit a couple feet. If you install this check valve (required), check the ejector pump manufacturer's instructions and see if you need to drill a 5/32" hole in the pump discharge pipe (level with top of pump and drilled so water will shoot out of the pipe at a downward angle) to prevent AIR LOCK of the pump, OK?

    Good luck!

    Mark