    Gfci electrical code for kitchens
    Are gfci outlets require
    Above all kitchen counters
  • May 24, 2014, 03:30 AM
    stanfortyman
    Yes. All receptacles serving counter areas must be GFI protected.
  • May 24, 2014, 05:19 AM
    donf
    Just to be a tad more specific, it is required that there be a minimum of two 20 amp. Branch circuits to serve countertop receptacles and the receptacles must be GFCI protected.

    The protection can be either by a GFCI circuit breaker or by GFCI receptacles protecting downstream receptacles. Or individual GFCI receptacles.